[Bldg-sim] ASHRAE
Bishop, Bill
wbishop at pathfinder-ea.com
Wed Oct 20 08:57:47 PDT 2010
Sambhav,
For baseline pump energy, you can adjust the mechanical efficiency of
the pump without affecting the autosized flow rate. In eQUEST, I adjust
the mechanical efficiency (usually reducing it to 0.52 +/-) to get
22W/gpm or 19W/gpm, as indicated in the PV-A report for pump power and
flow.
Sections G3.1.3.2 through G3.1.3.5 are for space heating hot water
systems. Domestic hot water requirements are found in Table G3.1, No.11
Service Hot-Water Systems.
A centrifugal pump "rides the pump curve" when it is a single-speed pump
(no VFD) but the system has at least some two-way valves to permit
variable loop flow. So, for example, in eQUEST you would model a
secondary pump riding the pump curve by setting the secondary CHW loop
pump capacity control to "One Speed Pump" and making sure some or all of
the CHW coil valves are "Two Way".
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of sambhav
tiwari
Sent: Tuesday, October 19, 2010 6:39 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE
Hi All,
In the ASHRAE-90.1-2004 it is menitioned that we have to
model chilled water pumps in baseline for 22W/gpm and hot water pumps
for 19W/gpm but there is no input in the software as W/gpm for the
pumps either we can enter gpm or watts seperatly then how can we
incorporate this for baseline?
In Page 182 G3.1.3.3 it is mentioned that hot water supply and return
temperature shall be 180 ansd 130F is this for boilers or Domestic hot
water heating system?
If in our proposed case DHW is electric type than can we show some
energy consumption difference for baseline DHW in terms of some
efficiency, insulation or temperature parameters or not ,or only if
our DHW is solar type than only savings can be claimed from
baselineDHW?
In Page G3.1.3.10 it is mentiond that chilled water oumos serving less
than 300TR shall be be modelled as primary/secondary system with
secondary pump riding the pump curve.I did'nt get what is meaning of
secondary pump riding the pump curve.
I shall be obliged if any one can give satisfactory answers to these
queries regarding ASHRAE.
Thanks
Sambhav.