[Bldg-sim] Unusual Result
Jaigath Chandraprakash
cjaigath at yahoo.com
Mon Sep 27 16:30:17 PDT 2010
Thank you Karen, Joe, and everyone for your advice.
To answer your question if the building has an economizer, no it does not have
an economizer. I have also asked the mechanical designer regarding the
electrical load in his design criteria and he did confirmed that his assumptions
are typical for this type of building. I am really tempted to adjust the
electrical load because it is too high compared to typical offices and I agree
with you Karen that equipment do runs only at a fraction of the day.
Thanks again,
Jaigath
________________________________
From: Karen Walkerman <kwalkerman at gmail.com>
To: Jaigath Chandraprakash <cjaigath at yahoo.com>
Cc: bldg-sim at lists.onebuilding.org
Sent: Fri, September 24, 2010 7:14:47 PM
Subject: Re: [Bldg-sim] Unusual Result
If most of your cooling loads come from internal loads as you said, then having
windows with a higher U-value allows the building to lose heat to the outside
any time it is cooler outside than inside. If you look at ASHRAE 90.1, the
requirements for windows changes dramatically as you move from colder to warmer
zones. In warmer zones, the allowed U-value is higher, but the SHGC is lower.
Also, it is usually good to verify that this is actually the case, often
installed equipment runs only a fraction of the day, or at a fraction of the
peak energy use. If your internal loads are not actually as high as you are
modeling, this could change things.
Lastly, does the building have an economizer? This may make sense for this
particular project.
--
Karen
On Fri, Sep 24, 2010 at 5:59 AM, Jaigath Chandraprakash <cjaigath at yahoo.com>
wrote:
The project I am working on is an office building that operates 20 hrs per day
with most of the loads occuring at night and low occupancy on daytime. It is a
cooled by a DX roof unit and has a very high internal load. No heating equipment
is required because the building is in Climate 1. I was surprised that when I
changed my window U-value from 0.3 to 0.7 I got less cooling consumption. I
always thought that getting low u-value will give me less coling consumption.
Can somebody tell me why I am getting less cooling when I use a higher window
U-value?
>
>Thanks,
>
>Jaigath
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100927/710db7ab/attachment-0002.htm>
More information about the Bldg-sim
mailing list