[Bldg-sim] eQuest - Model verification
Chuck Khuen
chuck.khuen at wxaglobal.com
Fri Apr 29 13:14:21 PDT 2011
As to James posting on this issue the weather data platform we are just finishing has cleaned up and localized weather input and can deliver a continuously updated stream of recent history and current conditions with direct web services access to any and all data. In other words, we have the weather data side of the client’s desire all set. We are very happy to cooperate with any efforts to integrate, assimilate or utilize this in a model or models. Indeed we are looking for partners here, as we believe this is going to be an increasingly important element in the solution to upgrading existing buildings. So if anyone wants to take on this part of the problem for Katherine, we will supply the weather data portion for free.
Chuck
_____________________
Chuck Khuen
Principal
Weather Analytics Inc.
www.weatheranalytics.com
781-856-5383
From: James V Dirkes II, PE
Sent: Friday, April 29, 2011 12:02 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest - Model verification
FYI, Check out www.Weatheranalytics.com for “AMY” (Actual Meteorological Year) data. They’re a new player in this arena and seem to have their act together.
The Building Performance Team
James V. Dirkes II, P.E., LEED AP, BEMP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: Jorge Torres-Coto [mailto:jtorres-coto at mbo1.com]
Sent: Friday, April 29, 2011 10:49 AM
To: 'Nick Caton'; 'James V Dirkes II, PE'; 'Karen Walkerman'; 'Carol Gardner'
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] eQuest - Model verification
5% is a really tight number we have been forced to work with on come retro commissioning projects in the past, with 10% being the norm on an annual and monthly basis for overall building energy use. Anything stricter than those numbers is unrealistic (again for the overall building).
Jorge E. Torres Coto
4830 Viewridge Ave.
San Diego, CA 92123
p 858.751.0933
f 858.751.0937
c 858.688.6088
--------------------------------------------------------------------------------
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Friday, April 29, 2011 7:42 AM
To: James V Dirkes II, PE; Karen Walkerman; Carol Gardner
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest - Model verification
I know I have less experience calibrating models than some other respondents, but I’ll share my perspectives as well:
It is easy to adjust occupancy schedules / lighting loads in eQuest, but it requires the end-user knows the program. If the end-user is inexperienced with eQuest or any other simulation program, then there is no “easily modifiable” model you can provide.
1) Even if I manage to put in daily occupant and fan schedules based on actual use, will the model be accurate enough to take me within 1%?
With regard to historical modeling, showing any deadband of accuracy to known costs/consumptions is *technically* possible given enough information and time… That said, falling within 1% of any holistic measure, even on an annual basis, before “refining the unknowns” would probably happen only by very lucky/happy coincidence. It’s fair to say that in a relative sense, some buildings operate much more regularly and predictably than others, and for these cases you or a client might reasonably expect a tighter deadband. Asking what is “accurate enough” is like asking “what’s reasonable,” and the answer is that it depends on what info/time you have. There are always “unknowable” variables that can play a big role in your end-results (example: what is the actual leakiness of a 35 year old envelope?).
2) We have been asked to remove plug loads (both for consumption purposes and cooling loads). Will this be too big of an assumption to get any accuracy out of the model in the future?
Depends on your building, but for most buildings plug loads are a significant fraction of consumption/internal loads.
3) How do I modify the weather input file?
I saved the attached email from David Reddy for the next time I need to tackle “actual weather.” My attempts thus far haven’t been terribly successful, so I have no “go-to” procedures to share just yet. I have heard reference from those who appear in the know to macro/VBA-heavy excel spreadsheets which can automate the workflow to one extent or another, but I’ve not yet seen one with my own eyes. I have yet to hear of any program that can “easily” incorporate recently recorded weather data.
4) Are there any other ideas I’m missing that will help us validate a model as an absolute measure of actual building energy consumption?
Generally: the only “absolute measure of actual building consumption” will be the utility bills. Something about the 1% number tells me you or your client might be trying to hammer a nail with a screwdriver… Energy models are great for looking to the past to make decisions that acknowledge the unknowns of the future, but if the real goal is to know the actual energy usage on an hourly basis – why not set up some sub-meters and track them? While meters/bills measure energy usage and energy models can use that information to make predictions, models don’t determine bills – it doesn’t work in reverse!
PS: For all the work you might put into calibrating a model with historical weather and other known data, keep perspective that your model will only ever be that accurate for behaviour in that year. The moment anyone wants to use this model predictively (for the future), you probably should swap back to TMY weather data and embrace the inherent unknowns.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V Dirkes II, PE
Sent: Thursday, April 28, 2011 7:12 PM
To: 'Karen Walkerman'; 'Carol Gardner'
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest - Model verification
Weighing in late on this….
If I get >80% R-squared correlation, I think I’m doing well!
There are so many unknowns, including the normal situation that the client doesn’t know their own operating schedules, occupancy patterns, or maintenance / calibration procedures….
The Building Performance Team
James V. Dirkes II, P.E., LEED AP, BEMP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Karen Walkerman
Sent: Thursday, April 28, 2011 3:31 PM
To: Carol Gardner
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest - Model verification
Also, a model that is calibrated to actual building use and weather can help to highlight building operation issues. I have had models which were off from actual operating energy use that I was able to determine how the building was operating inefficiently.
In one case, I created a model of an existing building. For this model, I made an actual count of lighting fixtures and computers. For most of the year, there were few other electrical loads. I based on their occupancy and use schedules, I was not quite able to calibrate the electrical energy use. When I met with the client, I informed him that my model showed somewhat lower electrical use, equivalent to 1/3 of the computers remaining on 24-hours per day. As it turned out, about 1/3 of the employees DID leave their computers on at all times so that they could log in remotely.
... I guess what I'm saying is that maybe the goal is not to get the model within 1% of the building energy use, but get the building within 1% of the model.
--
Karen
On Thu, Apr 28, 2011 at 3:20 PM, Carol Gardner <cmg750 at gmail.com> wrote:
Bill summed it up really well, Katherine. Sometimes a client will think a calibrated model must match the real building by an unrealistically high number, like 1%. I really can't imagine an instance when that would be desirable. It certainly would be costly to achieve.
Usually the plan is to use the calibrated model as a tool to examine various energy saving measures/opportunities that the client may be interested in implementing. It is important to remember, in this case that you are looking at the usage between the calibrated model and the ECM model, so the 1% deviation is consistent in both and not a worry.
Carol
On Thu, Apr 28, 2011 at 12:03 PM, Bishop, Bill <wbishop at pathfinder-ea.com> wrote:
Katherine,
The questions I would have for you (or your client) are:
· Is this an existing building, or something in the design phase?
· What is the model going to be used for?
· Is there something magical about the 1% number?
· 1% of what? Annual electrical consumption? Annual gas consumption? Both? Monthly electric/gas consumption? Monthly/annual electrical demand?
· Why remove the plug loads? Even if everything else is modeled perfectly, plug loads are typically 10% or more of annual electrical consumption but can be all over the place.
· “Easily adjusted” by whom? Does your client want you to hand them a model and let them make all subsequent adjustments?
Even if you are an expert energy modeler, and there is monitored energy data available for the building down to the individual electrical panels or broken out by end use (lighting, plug loads, individual HVAC units etc.) you will be hard-pressed to get to within 1% on a month-by-month basis. Even 5% month-by-month is difficult. Sure, you can tweak to your heart’s content to get a model to match annual electric consumption within 1% based on prior year’s utility bills but to maintain a calibrated model to that tolerance after that would require a lot of work.
I suggest searching the bldg-sim and equest-users archives for information about weather files.
Oh, one more question – how much money does your client have?
Regards,
Bill
William Bishop, PE, BEMP, LEED® AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
Error! Filename not specified.134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com www.pathfinder-ea.com
P Sustainability – the forest AND the trees. P
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Katherine Louman-Gardiner
Sent: Thursday, April 28, 2011 1:49 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] eQuest - Model verification
Hi All,
Our client would like us to produce an eQuest model that
a) Can be easily adjusted to include current and recently recorded weather data
b) Can be easily adjusted to reflect space occupancies and lighting loads
c) Will reflect the actual building energy usage to within 1%
Do any of you have experience trying to validate models like this?
My concern is that models are approximations, and will not account for small changes in occupancy, outdoor weather, etc.
I guess my questions are these:
1) Even if I manage to put in daily occupant and fan schedules based on actual use, will the model be accurate enough to take me within 1%?
2) We have been asked to remove plug loads (both for consumption purposes and cooling loads). Will this be too big of an assumption to get any accuracy out of the model in the future?
3) How do I modify the weather input file?
4) Are there any other ideas I’m missing that will help us validate a model as an absolute measure of actual building energy consumption?
Thank you for your help,
Katherine
Katherine Louman-Gardiner, EIT
Mechanical Engineer
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--------------------------------------------------------------------------------
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110429/2a2b95e3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1226 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110429/2a2b95e3/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14532 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110429/2a2b95e3/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110429/2a2b95e3/attachment-0005.jpeg>
More information about the Bldg-sim
mailing list