[Bldg-sim] DOAS and chilled beam/radiator

Paul Erickson perickson at aeieng.com
Mon Aug 15 06:33:55 PDT 2011


I¡¯ll add to the conversation.  I would agree with Vikram in that most chilled beam projects tend to be designed with constant volume primary air.  It simplifies the design and helps to reduce first cost.  If you do want to pursue VAV primary air then you (or the project engineer) should speak with the vendors you¡¯re considering to see how the beams perform at lower airflows (especially if you¡¯re expecting to get capacity from the beam when doing so).

Regarding 100% OA or RA, this decision has to consider a few things.  First, one has to acknowledge that the capacity of the beam per its given length is, among other things, dependant on the amount of primary being supplied to it.   Often this primary air cfm is greater than the minimum ventilation air needed, especially pronounced in perimeter spaces if loads are not minimized well.

Second, as was discussed in this string, the primary air must be capable of addressing the latent loads in the space.  Depending on your method of dehumidification (i.e. typical cooling coil, desiccant wheel, etc.), this may be a challenge with minimum ventilation airflow.  You¡¯ll need to consider how much primary air is needed.  If you find that more than the Min OA is needed, then you¡¯ll need to increase accordingly.

After you consider these two aspects, the primary airflow needed for achieving desired cooling capacity and the latent capacity of the primary air, then you¡¯ll need to evaluate the energy implications of at 100% OA vs. RA system.  You may find that you need a volume of primary air 2-3 times the OA needed,  thus doubling or tripling the amount of OA that is being conditioned if you choose the 100% OA approach.  Depending on climate and any airside energy recovery device, this can have a dramatic impact on energy consumption.

You asked some good questions. I¡¯d encourage you to work closely with the engineers doing the design so that you can talk through some of these items.

Good luck.

Paul Erickson  LEED(r) AP BD+C

5802 Research Park Boulevard | Madison, WI  53719

P: 608.236.1112 | F: 608.238.2614
perickson at aeieng.com<mailto:perickson at aeieng.com>  |  www.aeieng.com<http://www.aeieng.com>

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Monday, August 15, 2011 7:57 AM
To: Éò½à; near_ej at yahoo.com
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] DOAS and chilled beam/radiator


1.       In my experience - active chilled beams typically operate at constant volume (set to the ventilation rate in the room) and you vary the cooling rate with a 3-way valve on the cooling coil to vary the cooling capacity of the beam.

2.       Different beam designs have different induction ratios ¨C I would look up the manufacturers data. The typical range is around 3-6.

3.       Yes ¨C you can simulate a WSE now ¨C you need to add a chiller and select waterside economizer as chiller type. Not sure why your example is not working ¨C if you attach an inp file I¡¯m sure someone can shed some light no that.

Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society

From: Éò½à [mailto:shenjie820730 at hotmail.com]
Sent: Sunday, August 14, 2011 10:36 PM
To: near_ej at yahoo.com; Sami, Vikram
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] DOAS and chilled beam/radiator

Hi, Neeraj and Vikram:

Thanks for your promote advice. I'm reading DOE22Vol3-Topics.these days and found that IU's one application is just ceiling radiator .

Now, I have changed my system type to IU system with no separate MAU systems, but I still have two puzzles :
1) The fan control is gray which means you can't choose variable, so is it says that the fan is running the full power all the time?
2) How to define the induction ratio and make it reasonable? I'm not sure whether the recirculating air volume will affect the fan power. it seems not.

And another question is about water economizer? Can we simulate water economizer now?
For eQUEST 3.64, there are two methods, one is the water economizer in airside system, but the weakness of this water economizer is it will add the AHU fan power.
The other one is the water economizer chiller in waterside system, but it seems the function is not matural, I tried , but the hourly report shows the chillers still running in the winter for very low cooling load.

Thanks in advance.
Eleanor Shen

Date: Sat, 13 Aug 2011 02:11:07 -0700
From: near_ej at yahoo.com
Subject: Re: [Bldg-sim] DOAS and chilled beam/radiator
To: shenjie820730 at hotmail.com
CC: Vikram.Sami at perkinswill.com; bldg-sim at lists.onebuilding.org

Hello Eleanor,
Adding to Vikram's advice -- You may then also apply the heat recovery to the individual IU units instead of the DOAS.

But, an important question for experts who may be experienced with working real-life Chilled Beam systems is --

Whether or not the OA moved through the active chilled beams is completely (100%) Outside Air only OR Whether some of the supply air is still recirculated?
I presume it'll depend on latent loads but I understand that for most occupied zones some air is actually recirculated back to the AHU's to control the RH and balance the system!?
Please correct me if that is any different from anyone's real-life experience and what Vikram is referring to is the experience you all share? Vikram, your veiws?
We are modeling a couple of chilled beam and slab systems but with little live examples and experiences to corroborate on this aspect.

Your inputs would be valuable . . . .

Neeraj Kapoor
t: +91.99581.70018
Kalpakrit Sustainable Environments Pvt. Ltd.
New Delhi, India

On 12-08-2011 17:13, Sami, Vikram wrote:

If you are using an active chilled beam, then you don't need to model the doas - just use 100% OA for your ahu.

Sent from a mobile device

 -----Original Message-----

From:   Éò½à [mailto:shenjie820730 at hotmail.com]

Sent:   Friday, August 12, 2011 04:25 AM Central Standard Time

To:     bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>

Subject:        [Bldg-sim] DOAS and chilled beam/radiator

Hi, all£»

I¡¯m simulating a project with chilled beam/radiator plus dedicated fresh air system, I search from archive, it seems most of you using DOAS (a dummy zone) and IU/FCU to simulate, DOAS provide the fresh air and IU/FCU use the ¡°Outdoor air from¡± DOAS, the radiator use baseboard instead with zero fan energy power.

But the DOAS in my project is 1) variable speed to reduce the fresh air energy base on occupancy schedule; 2) wheel heat recovery with exhaust air; 3) during the transition period, the DOAS will bypass the wheel to provide maximum fresh air to offset all the heating and cooling demand and chilled beam and radiator will shut off.

Now, my method is :

1)  using VAV system to represent DOAS , enter the ¡° Design supply/return ¡° flow to show the DOAS fresh air and exhaust air volume;

2) Define the wheel heat recovery with fresh air and exhaust air, and operation control is ¡°OA exhaust DT¡±

3) Define the dummy with the same maximum fresh air volume, and also control the cool and heat temperature (otherwise the heat recovery will not work at all).

It seems works very well. But when I reading hourly report, I found the fresh air volume keeps the maximum all the time, so the fan running at the rated power the whole year, which results in the large fan energy consumpation.

How can I make the DOAS¡¯s fresh air volume variable and fan variable according to the acutal IU/FC¡¯s fresh air volume ??

Any comments and suggestions will be appreciated.

Eleanor Shen (Éò½à£©


Environmental Resources Management

Tel: +8621-5385 3050, ext:158

Fax: +8621-6469 2185

Email: eleanor.shen at erm.com<mailto:eleanor.shen at erm.com> <mailto:j at erm.com><mailto:j at erm.com>

www.erm.com<http://www.erm.com/> <http://www.erm.com/><http://www.erm.com/>

ERM Chinese Web Page

www.ermcn.com<http://www.ermcn.com/> <http://www.ermcn.com/><http://www.ermcn.com/>

*** ERM is granted Class A EIA License by China SEPA***

***ERM is named the 2008 Environmental Advisor of the Year (Acquisitions Monthly) ***

This email and any files transmitted with it are confidential and intended solely for the addressee.  If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.


Bldg-sim mailing list


To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110815/758c1685/attachment-0002.htm>

More information about the Bldg-sim mailing list