Reba Schaber Rschaber at PHMECH.com
Fri Aug 19 12:12:23 PDT 2011


Patrick,
I clearly understand that you can't change the outside air rate just because the system changes.  I'd like to explore the correct ventilation rate that should be used in both buildings.

ASHRAE 90.1-2007, section G3.1.2.5 states, Minimum outdoor air ventilation rates shall be the same for both the proposed and baseline building designs."

LEED 2009 reference guide, page 272 says, "Outdoor ventilation rates should be identical to proposed case."

When I've increased the ventilation rate by 30% for IEQc2, I have used the increased ventilation rate in both baseline and proposed.  I have not received any comments against that.  Has anyone else?  Even though the ASHRAE 62.1 calc may say the minimum ventilation required is 100 cfm, if I my drawings say "set the outside air damper minimum position to 130cfm," 130 cfm is then the minimum ventilation rate.

Is the quote from user's manual verbatim? "...the minimum ventilation rates designed for the proposed building must also be modeled the same..."  It uses the word designed.

Where does it say the 62.1 calculated rate has to be used?  Thanks for your feedback.

Reba

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Patrick J. O'Leary, Jr.
Sent: Thursday, August 18, 2011 9:46 AM
To: Michael A. Eustice
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] DOAS and baseline OA

in reality, i would agree with you.  if you were attempting to compare energy simulations for two different types of systems and were comparing the difference in outdoor air loads on system size/capacity (and costs of different systems) using the minimum per the different system types would be beneficial.

in leedality though the approach is a little different.  90.1 app g requires the minimum outdoor ventilation be the same to help prevent gaming the energy simulations, and is "enforced" by the leed reviewer's commenting on it.   the outdoor ventilation rate is the minimum designed outdoor ventilation rate.  so if the design is for a DOAS system then the minimum outdoor air rate for that system type is to be used in the baseline system.  same as if it the design were a packaged system but the baseline were VAV based on SF of the building (it happens) - the minimum oa rate would be what is designed for the packaged system.

except for the exception noted on page 182 when using dcv in the proposed if it is not required in the baseline.

look in the user's manual on page g-26, right column in the 1st ventilation paragraph, "outdoor air ventilation can be a major contributor to building energy consumption, but i is not considered an opportunity for energy savings under the performance rating method.  the minimum ventilation rates designed for the proposed building (not counting extra ventilation for economizer cooling) must also be modeled the same in both the baseline building and the proposed building."

in other words, in order to comply with the energy simulation requirements of 90.1 appendix g (the performance rating method) the minimum outdoor air rate has to be the same in both the proposed and baseline energy simulations (models).  so yes, outside of the one exception for dcv systems, the baseline outdoor air rate is the same as the proposed if you are only providing the minimum required per ashrae 62 regardless of what system type the baseline building is required to use.

On 8/18/11 7:47 AM, Michael A. Eustice wrote:
Unless I'm misunderstanding something, your sentence:

'when would the baseline be the same?  when you only provide the minimum required outside air per ashrae 62.'

Seems untrue to me.  Just so everyone is clear, under exact same conditions (occupancy, sqft, bldg type etc.), with the only difference being system type (VAV versus DOAS), the minimum required ventilation cfm required by ASHRAE 62.1 will be different.  The VAV system will almost always demand a higher minimum ventilation cfm, sometimes significantly more, since one zone can drive the system towards 100% outside air.

Michael

From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Patrick J. O'Leary, Jr.
Sent: Thursday, August 18, 2011 10:33 AM
To: Anne Juran
Cc: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] DOAS and baseline OA

note that 90.1 requires the <i>minimum</i> outdoor ventilation rates be the same in both the proposed and baseline models.  this is to prevent gaming of the baseline system sizes by adding capacity/increasing unit sizes which will increase baseline energy cost.

though the baseline ventilation rate(s) can be the same or less than the proposed they can't be more.

when would the baseline be the same?  when you only provide the minimum required outside air per ashrae 62.

when would they be different?  when you provide more outside air in the proposed design than is required by ashrae 62.
e.g.1  providing 30% more outdoor air than required to obtain 1 leed point via ieqc2 (increased ventilation)   (or using the international mechanical code ventilation rates if your local jurisdiction does not accept ashrae 62)
e.g.2  using evap cooling systems sized on air change rate by volume & 100% outdoor air.  ashrae 62 may require only 2,000 cfm but if you provide 20,000 cfm (based on space volume) then the proposed would have 20,000 cfm outdoor air and the baseline would have 2,000 cfm.  in a case such as this using 20,000 cfm in the baseline would require a very oversized unit that would use a lot more energy to condition the outdoor air and would reward you with more points under eac1/eap2.

On 8/18/11 7:03 AM, Anne Juran wrote:
I agree that the OA difference is extreme... I just let Trace run wild and do the calculation so I'm sure I have some crazy factors that would be adjusted for a "real" design.  In retrospect, I should have looked at it closer BEFORE submitting to USGBC.  I'm sure it made them closer at it, whereas if I was only slightly different they may have not questioned it.  Lesson learned!

It doesn't look like I'll get anywhere with USGBC, though, as the reviewer explicitly stated, "the total minimum outdoor air ventilation volume in the Baseline model must never be greater than the Proposed model."

Thanks for all the input!


From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jeremy Poling
Sent: Thursday, August 18, 2011 9:40 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] DOAS and baseline OA

While I don't intend to discuss the merits of VAV systems and know I'm part of a minority in that area, this is exactly why DOAS systems are being explored more right now on the research side (take for example the number of ASHRAE Journal articles on the topic over the past few years).  Without seeing your OA calcs I would also agree that the difference is more than I would expect between the two systems, but I'm more inclined to think the DOAS might be a bit low if it is being used in conjunction with FCUs.  VAV systems are typically underventilated due to two common mistakes in the calculations: not analyzing with the correct Ez and not using the minimum expected primary airflow for design purposes (refer to ASHRAE 62.1-2007 Section 6.2.5.1, specifically the note in that section).  When fixing these two typical mistakes in calculations without optimizing the primary airflow rates, I typically see OA requirements double from the incorrectly calculated values.

This situation is a good example of when to do one of two things (possibly both together)

If this is a LEED project, submit a project-specific CIR

Use section ASHRAE 90.1-2007 Section 2.5 Exceptional Calculation Methodology to get around the requirement and document the energy savings from reduced OA requirements for a DOAS system.

Jeremy R. Poling, PE, LEED AP+BDC

From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Mark Sorensen
Sent: Wednesday, August 17, 2011 11:42 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] DOAS and baseline OA

Anne,

While LEED/ASHRAE 90.1 requires the ventilation rates to be the same in both the Baseline and Proposed systems, the calculated difference for the two systems is much higher than expected. Suggest taking another look at the calculations and confirming that the critical zone for the VAV system has been properly determined and whether appropriate factors for the zone air distribution effectiveness (Ez) and system ventilation efficiency (Ev) have been applied.

Mark Sorensen
Diversified Energy Services
Fruitport, Michigan
231-578-1264

On 8/16/2011 9:12 AM, Jim Dirkes wrote:
Dear Anne,
I'm not sure why you think the OA requirement varies by system.  I'm not well versed in Standard 62, but my basic understanding is that one of the calculation methods is the result of building area and number of occupants.  Those are unchanged by system selection ... which is why it makes sense for Appendix G to require matching volumes.

The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Anne Juran
Sent: Tuesday, August 16, 2011 8:33 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] DOAS and baseline OA

I'm curious how everyone is handling the OA for Appendix G simulations when using a DOAS in the proposed system.  We have a design that is DOAS + FCU with a  total OA of 8,000 CFM.  When you run the OA calcs for this same building with a VAV system (the baseline), the total OA required to meet Standard 62 is 39,000 CFM.  This difference in OA represents a significant energy savings (in climate zone 4A), yet Appendix G requires the OA volumes to match.  It does not seem "fair" to me that the proposed case cannot take credit for design choice when it comes to OA.  I feel like Appendix G should make an exception for DOAS.  Am I missing something?  Is there a way around this?  Any thoughts are appreciated!

Anne







_______________________________________________

Bldg-sim mailing list

http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org

To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>






_______________________________________________

Bldg-sim mailing list

http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org

To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>




________________________________
The information contained in this message is intended only for the personal and confidential use of the recipient(s) named above. If the reader of this message is not the intended recipient or an agent responsible for delivering it to the intended recipient, you are hereby notified that you have received this document in error and that any review, dissemination, distribution, or copying of this message is strictly prohibited. If you have received this communication in error, please notify HT Lyons immediately, and delete the original message.

________________________________

No virus found in this message.
Checked by AVG - www.avg.com<http://www.avg.com>
Version: 10.0.1392 / Virus Database: 1520/3844 - Release Date: 08/19/11
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110819/ed52daff/attachment-0002.htm>


More information about the Bldg-sim mailing list