[Bldg-sim] ASHRAE 90.1 unmet load hours
Nick Caton
ncaton at smithboucher.com
Fri Dec 2 09:32:28 PST 2011
Very well put, Bill!
To Bill's first two bullets, I'll concur and further add that there are
cases wherein a space is intentionally and rationally not designed to
achieve ordinary comfort parameters. A clear example that springs to my
mind is auto-service garages, which I have seen commonly conditioned to
an extent, but not with the relatively tight deadbands expected inside
an office space. In such cases, for the specific purpose of
determining unmet hours in an energy model (which itself is ultimately a
means of checking the intended performance of the system is being
modeled), it's may be entirely appropriate to revise the parameters
defining an unmet hour, or to effectively remove that space from the
tally entirely.
I'll simultaneously re-emphasize Bill's final point: A significant
amount of unmet hours should always be treated first as a symptom
indicating a potential problem to identify and correct within the
modeled system/building behavior. Relaxing the parameters of what the
model is reporting for unmet hours should only be done judiciously and
on a space-by-space basis following the sort of logic we're discussing,
not liberally as a means of masking the symptom.
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bishop,
Bill
Sent: Friday, December 02, 2011 10:17 AM
To: Jim Dirkes
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 unmet load hours
Jim,
I concur with your understanding of how to define unmet load hours. Your
hotel poses challenges for meeting the unmet load hours requirement, as
you described.
Unfortunately this can be a difficult problem to solve, especially in
the proposed design where the actual HVAC system design might not be
able to handle the diversity of loads.
There have been a lot of good suggestions in the forums about how to
reduce unmet hours. I have a few general suggestions (by no means an
exhaustive list).
* For zones that are not controlled by a thermostat, or are only
loosely temperature-controlled by being next to a tightly-controlled
space, change to "unconditioned" or relax the thermostat setpoints as
Chris suggested.
* Use a lower heating setpoint for spaces that are heating-only
and not kept "comfortable", like stairwells, mechanical/electrical
spaces etc.
* Tweak the systems, especially at the zonal level - flowrates,
capacities, supply setpoints etc., while taking care not to deviate
substantially from the actual design.
* Back off from aggressive nighttime setbacks and/or model a
warmup period in the MIN-AIR-SCH if the unmet hours are when the system
fans first come on.
* Adjust space load amounts and schedules (occupancy, misc equip
and lighting).
* Use air walls where appropriate to even out loads/temperatures
between zones.
These suggestions assume that your systems are operating in the model as
you intend, and that we're not talking about thousands of unmet hours.
Most of these suggestions need to be applied to both the baseline and
proposed models and it is easy to lose track of changes if you're not
careful.
Some people advocate increasing the throttling range in problem zones
(in both baseline and proposed models), which always works because you
are redefining what "unmet hours" are. My opinion is that this should be
done only as a last resort since you are not actually improving the
modeled system performance.
Regards,
Bill
<mailto:wbishop at pathfinder-ea.com>
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chris Yates
Sent: Friday, December 02, 2011 9:40 AM
To: Jim Dirkes
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 unmet load hours
Hi james
Is it possible to relax your setpoints in proposed and baseline whilst
still meeting A55 requirements?
Would this help?
Chris
On 2 Dec 2011 14:32, "Jim Dirkes" <jim at buildingperformanceteam.com>
wrote:
Dear Forum,
Feedback requested, please! I've looked at some past posts on this
general topic and think I am asking about aspects not previously
discussed....
>From previous posts and my own understanding:
* If one or more zones is not meeting its setpoint in a given
hour, you have 1 unmet load hour. If 500 zones all fail to meet their
setpoint in one hour, it's till one unmet load hour.
* Add all such hours in a year to obtain your total unmet load
hours, which cannot exceed 8,760.
I am now modeling a hotel with:
* "Massive" wall elements in the lower floors with moderate
amounts of glass, "lightweight" construction in the upper floors with a
lot of glass
* Occupancy schedules that are all over the map for Office,
Assembly / Meeting Rooms, Kitchen & Restaurant, and Guest Rooms
* Individual HVAC systems for almost every occupancy type.
* Presentation to all points of the compass, especially the
Guest Tower, which is a 16-sided (roughly cylindrical) tower
This model is making my life very difficult trying to get unmet load
hours below 300! As I think about why that is happening, it strikes me
that the combination of mass, schedules and orientations are spreading
the unmet loads around to different hours than is normal for many
buildings. Can any of you share your thoughts about that perspective?
Thanks!
ASHRAE 90.1-2007
unmet load hour: an hour in which one or more zones is outside of the
thermostat setpoint range.
The real measure of a person's wealth is how much they're worth after
losing all their money.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111202/04721242/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111202/04721242/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 21646 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111202/04721242/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 13720 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111202/04721242/attachment-0005.jpeg>
More information about the Bldg-sim
mailing list