[Bldg-sim] Chiller size and number of ASHRAE 90.1
Alex Chapin
alexc at 2rw.com
Mon Dec 12 13:42:34 PST 2011
Process cooling loads need to be modeled with a separate chiller in the baseline and modeled with the same size, number, and efficiency as the process cooling chiller. If, however, an exceptional calculation is pursued then the proposed is modeled as designed and the baseline as that which is standard practice, thus providing an opportunity to take credit for a more efficient chiller than what is standard practice. Same approach applies to the process cooling loads themselves (i.e. you can take credit for more efficient utilization of process loads and efficiency of rejecting the process heat). I would recommend searching LEED Interpretations & Addenda Database for the official ruling on similar approaches so that you can learn what LEED is looking for as justification of documenting the basis for standard practice. https://www.usgbc.org/leedinterpretations/LILanding.aspx
Alex Chapin, EIT, LEED AP BD+C
Energy Engineer
2rw Consultants, Inc.
100 10th St. NE, Suite 202
Charlottesville, VA 22902
t: 434.296.2116 Ext. 305
2rw.com<http://www.2rw.com>
Date: Mon, 12 Dec 2011 20:00:49 +0800 (CST)
From: Esmireta <e2fye2 at 163.com<mailto:e2fye2 at 163.com>>
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Chiller size and number of ASHRAE90.1
Message-ID: <530d642e.46be.13432258ecb.Coremail.e2fye2 at 163.com<mailto:530d642e.46be.13432258ecb.Coremail.e2fye2 at 163.com>>
Content-Type: text/plain; charset="gbk"
Dear all,
According to the Table G3.1.3.7 of the ASHRAE90.1, the number and type of chillers could be determined. But I encountered a project of a industry factory, in which the industry process need a lot of cooling. I notice the Table G3.1.3.7 is for "Building Peak Cooling Load", I take it as the industry cooling will not be included in the Building Peak Cooling Load, is it correct? If so, is there any efficiency, number or type requirement of the industry chiller? Can I exclude the industry cooling energy in the building energy simulation?
Thanks!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111212/2ebf4dff/attachment.html>
------------------------------
_______________________________________________
Bldg-sim mailing list
Bldg-sim at lists.onebuilding.org<mailto:Bldg-sim at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111212/268fd7e9/attachment-0001.htm>
More information about the Bldg-sim
mailing list