[Bldg-sim] window opinions?
Nathan Miller
nathanm at rushingco.com
Fri Dec 16 08:15:45 PST 2011
Aaron,
It seems like the reviewers are just looking for SOME documentation of how
you established the U-Values for glazing. This is a LEED reviewer comment
from a recent project I was working on. Note that this was a LEED-NC v2.2
job, hence the reference to ASHRAE 90.1-2004:
"Please provide additional information to confirm that the framed assembly
U-value was used for the Proposed Case windows (e.g. showing that the
whole window assembly has been tested by NFRC, or verifying that LBNL
Window5 calculations have been provided for the whole assembly, or
verifying that the frame effects are captured within the energy modeling
software), or revise the model referencing ASHRAE 90.1-2004 Table A8.2 if
needed."
For this particular project, there was no NFRC or Window5 data available,
so we responded by giving them results both for the case where we entered
the center-of-glass U-value and defined the frame effect in eQUEST, and
then also the results for using the terrible default window assembly
U-values from 90.1 Appendix A. It made about a 5% swing in the energy
consumption, so obviously we hope they COG + frame effect results.
Nathan Miller, PE, LEEDRAP
Senior Energy Engineer/Mechanical Engineer
D 206-788-4577
<http://www.rushingco.com/> www.rushingco.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dahlstrom,
Aaron
Sent: Friday, December 16, 2011 6:56 AM
To: Bldg-sim2 (Bldg-sim at lists.onebuilding.org)
Subject: [Bldg-sim] window opinions?
Folks:
A quick survey:
Are people using the NRFC standard rating conditions (including standard
window unit sizes per http://www.nfrc.org/documents/1997_NFRC100.pdf Table
1 p15) for assembly u-factors for windows in the Proposed Case?
I know the ASHRAE 5.8.2.4 references the NRFC 100 test, but I'm debating
whether I should request custom calculations for my project's windows at
their actual size, or accept manufacturer's standard literature based on
the NRFC 100 rating sizes.
I know I can explicitly define the frame and glazing, which I prefer to
do, but sometimes it isn't an option.
Thanks,
Aaron Dahlstrom , PE, LEEDR AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414,
Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF:
215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com
<http://www.in-posse.com/> | akf web: www.akfgroup.com
<http://www.akfgroup.com/>
This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended recipient
of this e-mail, do not duplicate or redistribute it by any means. Please
delete it and any attachments and notify the sender that you have received
it in error. Unintended recipients are prohibited from taking action on
the basis of information in this e-mail. E-mail messages may contain
computer viruses or other defects, may not be accurately replicated on
other systems, or may be intercepted, deleted or interfered without the
knowledge of the sender or the intended recipient. If you are not
comfortable with the risks associated with e-mail messages, you may decide
not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111216/d48bcc7e/attachment-0002.htm>
More information about the Bldg-sim
mailing list