[Bldg-sim] Radiant Floor Temperature in EnergyPlus

Peter T. May-Ostendorp mayosten at Colorado.EDU
Thu Dec 29 15:24:30 PST 2011


Dear Mr. Sharma,

You are correct that there are no outputs specific to the radiant loop objects or the "InternalSource" constructions that will give you a surface temperature. However, you should be able to grab any surface's temperature with:

Output:Variable,
	SURFACE NAME,
	Surface Inside Temperature,
	Daily OR Hourly;

Regards,
Peter

____________________________________
Peter May-Ostendorp, EIT, LEED AP
PhD Candidate
University of Colorado at Boulder
College of Engineering and Applied Sciences
Building Systems Program
M: 970.426.8827

Please think before printing.

On Dec 29, 2011, at 2:31 PM, <bldg-sim-request at lists.onebuilding.org> wrote:

> Send Bldg-sim mailing list submissions to
> 	bldg-sim at lists.onebuilding.org
> 
> To subscribe or unsubscribe via the World Wide Web, visit
> 	http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> 	bldg-sim-request at lists.onebuilding.org
> 
> You can reach the person managing the list at
> 	bldg-sim-owner at lists.onebuilding.org
> 
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Bldg-sim digest..."
> <Today's Topics (1 messages).txt>
> From: Sachin Sharma <sachin5787 at gmail.com>
> Subject: [Bldg-sim] Radiant Floor Temperature in EnergyPlus
> Date: December 29, 2011 4:59:44 AM MST
> To: "'bldg-sim at lists.onebuilding.org'" <Bldg-sim at lists.onebuilding.org>
> 
> 
> Hi,
>  
> I am modelling a radiant hydronic floor cooling system. I want to know the floor temperature report on daily or hourly basis of my conditioned zone. I have tried finding the option in Output:Variable  object, but not able to find it. Can anyone help me out.
>  
> Thanks,
>  
> With regards,
>  
> Sachin Sharma
> M.Tech Energy Engg.
> Department of Mechanical Engineering
> NIT Jaipur
> +91 9983912512
>  
> 
> 
> <Digest Footer.txt>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111229/bd32b4ad/attachment-0001.htm>


More information about the Bldg-sim mailing list