[Bldg-sim] ASHRAE 90.1 - Appendix G - Parking Garages

Clark Denson cdenson at ssr-inc.com
Tue Jan 18 13:54:33 PST 2011


I would also add that, while lighting loads could be modeled differently
in the baseline and proposed models, ventilation fans should be modeled
identically.  One exception to that would be if proposed fan motors
exceed minimum motor efficiencies in Table 10.8.  Another possible
exception might be if ventilation fans were equipped with VFDs and
automatically controlled by carbon monoxide sensors, but you'd have to
prove your savings through an Exceptional Calculation Method.

 

Clark Denson, PE, CEM, LEED AP

SSRCx(r), LLC

(615) 383-1113

 

From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com] 
Sent: Tuesday, January 18, 2011 9:16 AM
To: Nick Caton; Richard Auffermann; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 - Appendix G - Parking Garages

 

While parking garages may not be considered "spaces" per ASHRAE, I think
lighting should still be modeled differently for baseline and proposed
per Appendix G, and not considered a process load. "Lighting power for
parking garages and building facades shall be modeled" per Table G3.1,
and baseline lighting is determined per Section 9.2, where values for
parking garage lighting power appear in both the Building Area and
Space-by-Space Tables. You could attach these (different) lighting loads
directly to a meter, as Nick suggests, if you don't model the parking
garage as a space in the model.

 

~Bill

 

William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP

Mechanical Engineer

 

 134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114                F: (585) 325-6005

wbishop at pathfinder-ea.com           www.pathfinder-ea.com
<http://www.pathfinder-ea.com/> 

P   Sustainability - the forest AND the trees. P 

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Monday, January 17, 2011 6:07 PM
To: Richard Auffermann; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 - Appendix G - Parking Garages

 

These definitions came up during review of one of my recent LEED
projects.  For future reference, 90.1 questions may be seen by a group
more keen to respond if you post to the [bldg-rate] list.

 

I've got a definite position if you'd like to hear:

 

1. As you point out, per the definition of "unconditioned space,"
parking garages are "...not considered enclosed spaces."  Whether in
design it's actually conditioned or not has no bearing on this
statement.

 

2. All of the definitions for space classifications, and indeed the
definition for "space," start with "an enclosed space..."  Therefore no
parking garage can be considered "conditioned" or "semiheated," or even
as a "space." 

 

3. This also means by extension (re: section 5.1.2): There are no
envelope requirements for parking garages, as they are not "spaces" of
any classification.

  

If you reject this approach and instead assert a parking garage can be a
"conditioned space," you'd be forced down a path of assigning identical
heating/cooling systems to parking garage spaces in both proposed and
baseline models, per Table G3.1.1.b, regardless of whether it's actually
conditioned or not.  Things might get hairy if you're only heating or
only cooling (I believe the other would need to match the baseline
serving the rest of the floor/building, as may apply).  I'd only suggest
that requiring heating/cooling of parking garages in all climates seems
odd for an energy efficiency standard - you'd have to explain that one
to me ;).

 

If you do have heating and/or cooling for a parking garage design, I'd
personally stick with points #1/#2 above and simply model such energies
as a process load alongside any mechanical ventilation systems,
identical in both models.  

 

I personally use eQuest, and prefer to model parking garages as simply
as a series of building shades with a series of process/lighting loads
attached directly to the meter.

 

All this is my take on the situation.  I think it's pretty defensible,
but there may have been CIR's I'm unaware of to the contrary - not that
precedent matters anymore...

 

Hope that helps you and others,

 

~Nick

 

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Richard
Auffermann
Sent: Monday, January 17, 2011 3:44 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 - Appendix G - Parking Garages

 

I have a questions about the modeling of Parking Garages for ASHRAE 90.1
Appendix G energy model

 

As I was looking up the definition of a conditioned and semi-heated
space in Section 3 of ASHRAE 90.1 I noticed that under the definition of
an "unconditioned space" it states that "Crawlspaces, attics, and
parking garages with natural or mechanical ventilation are not
considered enclosed spaces." In addition the definition of "ventilation"
is "the process of supplying or removing air by natural or mechanical
means to or from any space. Such air is not required to have been
conditioned." Since the air is not required to be conditioned then the
air can or cannot be conditioned, does that mean that any parking garage
conditioned or unconditioned is not considered an enclosed space? If
that is true then how do you model a parking garage since all spaces are
defined as being enclosed?

 

Richard Auffermann

Design Engineer

DAGHER ENGINEERING, PLLC

29 Broadway, New York, NY 10006

T. 212.480.2591 x122

F. 212.480.2654

rauffermann at dagherengineering.com

www.dagherengineering.com

 

Save Trees, Consider the Environment. Please print only when necessary.

 

This email and any attachments may contain confidential or proprietary
information and use or distribution is strictly prohibited. If you are
not the intended recipient, please notify us and delete.  Dagher
Engineering, PLLC has no responsibility for errors or discrepancies that
may occur in the electronic transmission of data.

 

_______________________________________________

Bldg-sim mailing list

http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org

To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110118/df8c81b7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110118/df8c81b7/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110118/df8c81b7/attachment-0005.jpeg>


More information about the Bldg-sim mailing list