[Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1

Larry Degelman ldegelman at suddenlink.net
Wed Jan 26 06:45:25 PST 2011


?Toilet room minimum exhaust rates are shown in Table 6-4 or Standard 62.1-2004 (sub-notes D and E.)

A side note:  Eight (8) air changes per hour translates to 2.67 cfm/sq.ft. if we a assume ceiling height of 20 ft.  This definitely sounds like a recommendation for cooling and not just ventilation.

LOD
===========================
Larry O. Degelman, P.E.
Professor Emeritus of Architecture
Texas A&M University
ldegelman at suddenlink.net
===========================


From: Ashraf Khan 
Sent: Wednesday, January 26, 2011 8:24 AM
To: 'James V Dirkes II, PE' ; bldg-sim at lists.onebuilding.org 
Subject: Re: [Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1


James,

 

If we introduce 0.06 cfm.sqft, of outdoor air, if it complies with ASHRAE requirements, then we can do that.  Normally all warehouses here will be having ventilators to exhaust air which is assumed that air intake by infiltration.

 

Also project is located in DUBAI, UAE. Climate here is very hot and humid; if I introduce outdoor air it will affect the storage materials in the warehouse. 

 

Did you know where can I find the exhaust rates, such as Toilets, Generator Room, pump room in ASHRAE?

 

Thanks & Regards,

Ashraf

 


--------------------------------------------------------------------------------

From: James V Dirkes II, PE [mailto:jvd2pe at tds.net] 
Sent: Wednesday, January 26, 2011 5:26 PM
To: 'Ashraf Khan'; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1

 

Ashraf,

 

It seems that all you need to do is demonstrate that your ventilation system complies with Table 6-1.  Are you introducing at least .06 cfm/sq.ft of outdoor air with the mechanical ventilation system?

 

If so, just document it!  If not, you're in trouble and will need to provide a ventilation system.

 

 

 



 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: Ashraf Khan [mailto:ashraf at mecsd.com] 
Sent: Wednesday, January 26, 2011 8:15 AM
To: 'James V Dirkes II, PE'; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1

 

Hello James,

 

I accept that ASHRAE 62.1 is concerned with people, the same we explained to LEED Reviewer team, this is the comment we received, 

 

However, since the project uses ventilator fans it is considered a mechanically ventilated space. Additionally, the LEED-NC v2.2 IEQp1 CIR ruling dated 10/8/2008 states that unless the mechanically ventilated warehouse has no human occupancy except for maintenance and repairs it must meet the requirements of ASHRAE Standard 62.1-2004. The narrative states that the warehouse will be occupied for the loading and unloading of goods; therefore, the warehouse is regularly occupied. 

Provide calculations for the warehouse space demonstrating that the space complies with the minimum requirements of ASHRAE Standard 62.1-2004.

 

I am not having any idea how to convince the team.

 

Thanks & Regards,

Ashraf


--------------------------------------------------------------------------------

From: James V Dirkes II, PE [mailto:jvd2pe at tds.net] 
Sent: Wednesday, January 26, 2011 3:46 PM
To: 'Ashraf Khan'; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1

 

Ashraf,

 

ASHRAE 62.1 is concerned with people, who need ventilation (supply / intake).  For typical buildings, you may not need separate exhaust fans, because that amount can probably exfiltrate through cracks.  Supply and exhaust fans can be used in tandem if the building is fairly tight (no leaks).

 

Your MEP team's  5-8 air changes per hour is for cooling, not ventilation.  Any building with which has that much infiltration is closer to a tent than a building! (It's not closed up.)

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ashraf Khan
Sent: Tuesday, January 25, 2011 11:55 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Warehouse ventilations to comply with ASHRAE 62.1

 

We received a LEED review comment regarding Warehouse ventilation to comply with ASHRAE 62.1-2004.

 

Generally depending on the warehouse storage, MEP team recommends 5-8 Air Changes per Hour by thumb rule for exhaust and air intake is assumed by infiltration by windows, open doors etc.. But this number I haven't find in ASHRAE, please give me reference.

 

ASHRAE 62.1-2004, Table 6-1 for warehouse category says to have 0.06 cfm/ft2, is this number defines to intake or Exhaust? If it is exhaust, it is too small as volume of warehouse will be high.

 

Please share your ideas to comply with the requirements.

 

Thanks & Regards,

Ashraf



--------------------------------------------------------------------------------


_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110126/1172767a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 43145 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110126/1172767a/attachment-0002.jpeg>


More information about the Bldg-sim mailing list