[Bldg-sim] insulation film on windows in EnergyPlus
Pedro Peixeiro
ppeixeiro at lnec.pt
Tue Jul 12 02:03:27 PDT 2011
Jeong,
Shading coefficient is an older term that has been gradually substituted
by the SHGC value. The object WindowMaterial:SimpleGlazingSystem allows
you to enter this value directly. A quick search around the web shows
that the SC should be around 1.15 * SHGC. But you should get some more
reliable information on this. Also, it is recommended that you use the
detailed input for windows and not the simple glazing system. If you
can, get a hold of the solar transmittance and conductivity of your
window and you should be able to use the detailed input.
Pedro.
On 11-07-2011 6:11, ??? wrote:
> Hello,
>
> I'm running simulation wih EnergyPlus.
> In order to apply ECMs, I'm trying to apply insulation films to each
> window.
> The object I used is *WindowMaterial:Shade*, but I don't think my way
> is correct.
> I have limited information (Available data include solar reflectance,
> visible reflectance/transmittance, and shading coefficient),
> which is further complicating the situation.
>
> Any help will be much appreciated.
> Thank you.
>
>
> _Jeong
>
> p.s. BTW, I do not understand why there's no shading coefficient
> field in window-related objects.
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110712/2f702065/attachment-0001.htm>
More information about the Bldg-sim
mailing list