[Bldg-sim] JWT Q2 - Energy Plus Calibration Experience
Jim Dirkes
jim at buildingperformanceteam.com
Thu Jul 21 10:49:06 PDT 2011
Dear Josh,
As a start, "as-built" should really be "as-measured" by you or a reliable
tech.
The "measured" values should include:
. Power for all major equipment
. Flow for all major fans and pumps
. Zone and discharge air temp setpoints
. Schedules of (real) operation (If you have a BMS which trends
operation, that's a good place to start. If not, plan to talk to
knowledgeable people)
. Actual weather (you might check out www.weatheranalytics.com)
. There will still be unknowns / unknowables, such as infiltration.
Those can be adjusted within reasonable limits for a better fit.
. Start by narrowing down the list of variables that are not know
with certainty and do NOT assume that things are as shown on plans!
p.s., I've worked up an interface between GenOpt (Dr. Michael Wetter at
LBNL) and E+ which makes iterative runs of E+ until it has a "Best fit".
It's still in the "development" stage, but seems to work well. Please send
a private message if you're interested in trying it out.
The Building Performance Team
James V. Dirkes II, P.E., BEMP , LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Talbert, Joshua
Sent: Thursday, July 21, 2011 11:07 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] JWT Q2 - Energy Plus Calibration Experience
Good Morning Sim Board,
The project I am working on requires a level of calibration between my
AS-BUILT simulations and metered data for the facility. Would anyone please
be able to comment on their previous calibration experiences? Does E+ tend
to simulate certain loads under or over for instance? Do systems/components
tend to run true to their real life equivalents, or are similar deviations
common?
Thank you,
Josh
Joshua W. Talbert P.E., LEED-AP
Mechanical Engineer
Hallam///ICS
38 Eastwood Dr. Suite 200
S. Burlington, VT 05403
P: (802) 658-4891
F: (802) 658-1457
_____
CONFIDENTIALITY NOTICE:
The information contained in this transmission, as well as any accompanying
documents, constitutes confidential and/or legally privileged information
which is the property of Hallam-ICS. The information is intended solely for
the individual entity named on this transmittal sheet. If you are not the
designated recipient, you are hereby notified that any disclosure, copying,
distribution or taking any action in reliance on this information is
strictly prohibited. If you received this in error, please contact the
sender and delete the material from any computer. Opinions, conclusions and
the information in this message that do not relate to the official business
of my firm shall be understood as neither given nor endorsed by it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110721/b72bcba5/attachment-0002.htm>
More information about the Bldg-sim
mailing list