[Bldg-sim] Snow melt (UNCLASSIFIED)
Bishop, Bill
wbishop at pathfinder-ea.com
Mon Jul 25 08:08:19 PDT 2011
John,
While I appreciate the relative novelty of a snow melt system for balancing annual ground loop temperatures, there are a couple ideas that shouldn't be excluded outright when considering server cooling loads: higher cooling temperatures and air-side economizers. The control strategies and equipment for economizers are well-established, and their use is becoming more common in datacenters despite concerns about contaminants and humidity control. A conservative supply air temperature is 75°F, with ASHRAE TC 9.9 recommendation as high as 80.6°F. Google, Intel and Microsoft have all had good experimental results even with 90°F and above, and with little to no humidity control. I also second Carol's suggestion of heat pump space heating and DHW.
The servers might have a different opinion:
http://dilbert.com/strips/comic/2011-07-24/
Regards,
Bill
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Friday, July 22, 2011 6:30 PM
To: Carol Gardner; David Eldridge
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Snow melt (UNCLASSIFIED)
Hey Carol,
In a majority of 4-season climates (here in Kansas City too), I'd expect you would not use such a secondary loop in the dead of summer where night-time temperatures would not drop to practical/conducive levels for heat rejection.
But to answer your question from other angles: this heat rejection/heat gain loop would help in the summer months decades down the road, where you've avoided overcooling/overheating the ground temperatures over time.
It would also help in that through late spring and early summer, you would be able to cool through the workday/evening, then use cooler nighttime/morning temperatures to offload the extra heat built up on a daily basis, resulting in cooler net temperatures day-to-day. This would ultimately reduce and forestall the maximum temperatures that would be reached during mid-to-late summer when you'd want this transfer loop shut off 24/7.
I'll be digging into that OSU link David, thanks for the heads up!
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Carol Gardner
Sent: Friday, July 22, 2011 4:52 PM
To: David Eldridge
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Snow melt (UNCLASSIFIED)
I was wondering how the snow melt system would work help you during the summer months, unless you are up in the mountains somewhere. What about preheating, or just heating, DHW as it would be a year round load?
On Fri, Jul 22, 2011 at 2:46 PM, David Eldridge <dse at grummanbutkus.com> wrote:
Check the Oklahoma State Building and Environmental Thermal Systems
Research Group -- there are a number of papers on various topics related
to geothermal systems in hybrid, shallow, and other configurations.
http://www.hvac.okstate.edu/
There is also a great research project where snow melt was the primary
purpose of the geothermal system, which is not quite what you guys are
after but might offer some guidance.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Friday, July 22, 2011 4:26 PM
To: Eurek, John S NWO; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Snow melt (UNCLASSIFIED)
I will say I got really excited this past year about the isolated idea
of combining snow melt with geothermal well field design...
For those unfamiliar, well fields in this part of the Midwest (KS/MO/NE)
historically heat up over the long haul, especially with intense
equipment loading like John's situation... fields installed decades ago
commonly end up struggling and failing when the extreme summers roll
around, sooner or later.
The most common pre-emptive/patch solution I've seen to tackle this
trend is to tack on (or set up infrastructure for) an exterior dry
cooler to reject excess heat from the loop.
I pushed hard recently to consider a "snow melt" loop (even if not used
to functionally melt snow) as a better "free" means of keeping a
well-field in balance annually, but the real trick is in how to set it
up so that this extra loop it doesn't require active
maintenance/monitoring... Making a location for horizontal loops like
this is also a challenge in many cases where the land is not readily
available or has future expansions planned. Most clients out there,
even those with motivated maintenance staffing, would really be best
served with a "fire and forget" system that could handle itself decades
down the road without requiring active monitoring/adjusting as the
seasons change and temps swing. Ultimately, I haven't yet come up with
any particularly great setup that I would consider fool-proof over the
span of decades, but I'd be very interested if others have
thoughts/details to share on how this might be achieved.
Conceivably, and to your specific questions John, I'd speculate the
actual controls would at a minimum need to define parameters
establishing a range of "target" loop temperatures for the cooling and
heating season (these would be based on 1st year loop simulations, to
start). The "melt" loop routed near the surface (or embedded in
concrete where it might be safe), would be normally closed, but valves
would open for circulation when the outside temperatures* are conducive
to pushing the well field return temperatures in the desired direction.
Done cleverly, you could push the system to permit water below the
setpoint during the cooling season, and above the setpoint during the
heating season as well (this behavior would potentially occur in the
swing seasons - spring/fall). I'm thinking the ideal controls would
constantly monitor and take advantage of free heat rejection & free heat
gains whenever applicable.
* Another point to consider: What temperatures are ideal to monitor for
such a loop? Outside air data may be easily available, but considering
the lag in topsoil temps and depending on what you choose for the actual
loop installation location you might do better to locate a sensor
elsewhere... A loop underneath black asphalt getting will experience
different temperatures than the same loop embedded in light-colored
hardscape or simply under exposed topsoil.
Northern climates might find the same setup of interest to primarily
gain free heat gain to keep loops in balance, routing the secondary loop
through building envelopes or similar massed structures that would pick
up extra heat in the summer months.
Suffice to say I find it an interesting topic - if anyone has ever come
across a design guide or white paper on this subject I'd also be very
interested to hear about it!
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Eurek, John
S NWO
Sent: Friday, July 22, 2011 3:30 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Snow melt (UNCLASSIFIED)
Classification: UNCLASSIFIED
Caveats: NONE
Modelers.
One of my projects has server rooms which combined produce 143 MBH (more
heat
than some home furnaces) and the servers run all the time.
I am designing a ground source heat pump system for the building. The
energy
model shows that the geothermal well field is unbalanced by 522,500,000
btu.
I'm plan on using a snow melt system to get rid of the extra heat. (Snow
melt
is a nice by product, the goal is to balance the well field's annual
load.)
Has anyone designed this kind of system?
I'm not really sure how to model it?
I'm foggy on how to control it so I get rid of just the right amount of
heat.
Has anyone designed this kind of system?
It is fun to get to design energy efficient systems and coming up with
new
ideas, but it is hard to do research on them. (I know snow melt isn't
new,
geothermal isn't new, computer room cooling isn't new, but I haven't
found
any articles tying the three together.)
John Eurek PE, LEED AP
Mechanical Engineer,
US Army Corps of Engineers
Omaha District CENWO-ED-DA
1616 Capitol Avenue
Omaha, NE 68102
Phone: (402) 995-2134 <tel:%28402%29%20995-2134>
email: john.s.eurek at usace.army.mil
Classification: UNCLASSIFIED
Caveats: NONE
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110725/1d8defab/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110725/1d8defab/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110725/1d8defab/attachment-0005.jpeg>
More information about the Bldg-sim
mailing list