[Bldg-sim] Balcony Heat Loss
Brian Fountain
bfountain at greensim.com
Fri Jun 17 07:39:04 PDT 2011
The accepted workaround is to add another wall type that is comprised of
12" of just concrete (U = 5.5 W/sq-m C) and has a height equal to your
slab thickness -- say 6". So the area would be the wall length x the
slab thickness.
Not sure if this is clear -- it is better described on page 7-9 of the
EE4 modelling guide.
Brian
On 6/17/2011 10:20 AM, Aaron Smith wrote:
>
> Hello,
>
> When performing energy modeling to determine compliance with the
> Canadian Energy Code (MNECB), penetrations through the building
> envelope must be taken into account when calculating wall R-values if
> their area exceeds 2% of envelope area. I'm working on a LEED project
> and trying to calculate the wall R-value of a Hotel taking into
> account heat losses from the balconies which are extensions of the
> floor slab (balcony penetrations exceed 2% of envelope area).
>
> I realize this is a rather complex heat transfer problem but hope
> there may be an easy approximation. My first thought was to treat
> them like a parallel path heat transfer problem: 1/Req = %slab/Rslab +
> %wall/Rwall but I'm thinking that may not be fair (perhaps this would
> be used if you had concrete studs in the wall). My other thought is
> to treat the slab penetrations as a separate wall type (uninsulated
> concrete wall) -- this would have a reduced affect on the overall wall
> R-value.
>
> Does anyone have thoughts on this?
>
> Thanks,
>
> Aaron
>
> **Aaron Smith, **//P.Eng //
>
> /LEED® AP BD+C,//M-ASHRAE, Mechanical Engineer/
>
> t: (902) 422-7393
>
> f: (902) 423-4945
>
> e:asmith at mreng.ca <mailto:asmith at mreng.ca>
>
> The electronic message contained herein is private and confidential,
> intended only for the recipient(s) specified. If you have received
> this message in error, please delete it and notify us immediately.
> Any accompanying files are supplied as a matter of courtesy only. The
> data are without warranty of any kind. Any person or business making
> use of the data is responsible for confirming its accuracy and
> completeness. M&R Engineering Ltd. is not responsible for edited or
> produced versions of this digital information.
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1382 / Virus Database: 1513/3709 - Release Date: 06/17/11
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110617/dbe7b707/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1860 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110617/dbe7b707/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list