[Bldg-sim] Appendix G - Fan power

Tyler Thumma tyler at energyopportunities.com
Tue Mar 8 10:14:08 PST 2011


That is correct. This issue has been fixed in the updated spreadsheet
attached.

 

Tyler Thumma, EIT, LEED AP

Energy Opportunities, Inc/a 7group Company

1200 E Camping Area Rd, Wellsville, PA 17365

thumma at sevengroup.com

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rosenberg,
Michael I
Sent: Tuesday, March 08, 2011 12:38 PM
To: jtorres-coto at mbo1.com; 'Sami, Vikram';
'bldg-sim at lists.onebuilding.org'
Subject: Re: [Bldg-sim] Appendix G - Fan power

 

A word of caution if you are using this 2007 tab of this spreadsheet.
The pressure credit is being calculated for the entire supply fan cfm.
It should only be calculated for the design airflow through the device.
While these two airflows can be the same, often they are not. 

 

Mike

 

__________________________

 

Michael Rosenberg, CEM, LEED AP 

Senior Research Scientist

ENERGY & ENVIRONMENT DIRECTORATE 

 

Pacific Northwest National Laboratory 

2032 Todd Street 

Eugene, OR 97405 

(541) 844-1960 

michael.rosenberg at pnl.gov <mailto:michael.rosenberg at pnl.gov>  

www.pnl.gov <http://www.pnl.gov/> 

 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jorge
Torres-Coto
Sent: Tuesday, March 08, 2011 8:29 AM
To: 'Sami, Vikram'; 'bldg-sim at lists.onebuilding.org'
Subject: Re: [Bldg-sim] Appendix G - Fan power

 

Yes that is correct, the dot means multiplication.

 

The Excel calculator will come in very handy (credit to 7 Group)

 

Jorge E. Torres Coto    

4830 Viewridge Ave.

San Diego, CA 92123

p              858.751.0933

f               858.751.0937

c              858.688.6088

 

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sami,
Vikram
Sent: Tuesday, March 08, 2011 8:11 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Fan power

 

Does the dot in the equation indicate multiplication? So should the
equation read CFMS X 0.0013 + A?

 

The reason I am confused is that they use X in other places. 

 

 

Thanks in advance

We've moved!  Please note our new address. 

Vikram Sami, LEED AP BD+C

Sustainable Design Analyst

1315 Peachtree St. NE, Atlanta, GA 30309

t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com
www.perkinswill.com <http://www.perkinswill.com/> 

Perkins+Will.  Ideas + buildings that honor the broader goals of society

 

Perkins+Will is carbon neutral. Learn more about our 2030 Challenge
Estimating + Evaluation <http://2030e2.perkinswill.com/>  tool for
fossil fuel free buildings 

 

This email and any files transmitted with it are confidential and
intended solely for the addressee.  If you are not the named addressee
you should not disseminate, distribute, copy, or alter this email.

 

________________________________

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1204 / Virus Database: 1497/3490 - Release Date: 03/08/11

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1226 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14532 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 47671 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment-0003.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 7group Appendix G Fan Power Calculator.xls
Type: application/vnd.ms-excel
Size: 130560 bytes
Desc: 7group Appendix G Fan Power Calculator.xls
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110308/47e5abeb/attachment-0001.xls>


More information about the Bldg-sim mailing list