[Bldg-sim] Parallel Units for LEED

Jorge Torres-Coto jtorres-coto at mbo1.com
Mon Mar 7 07:10:55 PST 2011


You only model them as they are supposed to run (one at a time or both at
the same time). 

 

You mention they run in parallel, so I assume that the capacity of both may
be required at peak load.  If they operated lead/lag, then you would only
model one (or half AHU capacity per floor).

 

Jorge E. Torres Coto   

4830 Viewridge Ave.

San Diego, CA 92123

p              858.751.0933

f              858.751.0937

c              858.688.6088



  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of varun kulkarni
Sent: Monday, March 07, 2011 6:38 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Parallel Units for LEED

 

Hello All,

 

I am trying to model a three floor office building for LEED V3. The first
and second floor are served by two chilled water air handlers, both
manifolded and running in parallel.

Does LEED require to model both the units because the schedules and drawings
show two units.

For baseline, I know ASHRAE G3.1.1 states I have to have seperate HVAC
system for each floor, as I have system 5.

-- 

Thanks and Best Regards,

 

Sincerely,

Varun Kulkarni , M.S. , EIT

RMF Engineering

5520, Research Park Drive, Suite 300

Baltimore, MD - 21228

 

Office : 410-576-0505 ext. 5352

Mobile: (+1)405-385-1928

 

Note: Please do not print, unless required.

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110307/2687f039/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1226 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110307/2687f039/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14532 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110307/2687f039/attachment-0002.gif>


More information about the Bldg-sim mailing list