Raj,

 

This is where Section G2.5 comes in - you can model the night purge as
an exceptional calculation methodology and take credit for it that way.
It will require a parametric model or even a third model (depending on
your approach to parametric models).

 

Jeremy R. Poling, PE, LEED AP+BDC



 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kris Raj
Sent: Friday, March 18, 2011 9:20 PM
To: Bldg-sim
Subject: Re: [Bldg-sim] Night purge

 

James,

           Thank you for your responce. I am really confused because
having night purge requires that the base case and proposed case have
different operating schedules. The proposed case controls will check the
space and outdoor temperatures at night and run the fans.

However for the base case the fans are turned off at night. Dosen't
ASHRAE 90.1 appendix G require us to have the same operating schedules
for the base and proposed case.

 

thanks,

raj

 


 

 

________________________________

From: "James V Dirkes II, PE" <jvd2pe at tds.net>
To: Bldg-sim <bldg-sim at lists.onebuilding.org>
Sent: Fri, March 18, 2011 8:09:44 PM
Subject: Re: [Bldg-sim] Night purge




Dear Raj,

If it saves energy, it counts.

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kris Raj
Sent: Friday, March 18, 2011 6:32 PM
To: Bldg-sim
Subject: [Bldg-sim] Night purge

 

Hello,
Does anyone know if we can take credit for night purge under LEED 2.2
thanks,
raj

 

 