[Bldg-sim] slab on grade answer
Patrick J. O'Leary, Jr.
poleary1969 at gmail.com
Tue May 17 14:00:16 PDT 2011
i just received a clarification about the f-factor for 4" slab on grade
vs 6" slab on grade for the purposes of leed review. the usgbc response
(through the website/contact section) is:
"Thank you for your technical customer service inquiry regarding LEED-NC
v2009: EAc1. It is assumed that you are following the Performance
option (Option 1) of EAp2 & EAc1, using Appendix G of ASHRAE 90.1.
Yes, the 4" slab (modeled & specified) should meet the requirements for
LEED purposes. Please note that there is no F-factor requirement listed
as part of the Mandatory provisions of Section 5.4; it is only listed
for the Prescriptive approach requirements of section 5.5, which is not
necessary for LEED EAp2/EAc1 compliance.
If you model the slab as a 4" slab with 12" of earth (0.75 soil
conductivity) underneath it in the Proposed Case model, the energy model
should indicate the U-value of this slab. You could simply state in
your submittal (4" slab modeled with 12" of earth with 0.75 Btu/h-ft-°
soil conductivity, U-value calculated within energy model as x.xx).
Please be careful to avoid the common mistakes of modeling the slab
without any earth beneath it, or modeling the Baseline slab "U-value"
using the "F-factor" values from Tables 5.5-1 - 5.5-8. F-factors and
U-values are not interchangeable, of course. Also, if the energy model
cannot reflect an F-factor, please model the Baseline slab-on-grade
floor as a 6 inch concrete slab over earth with a soil conductivity of
0.75 Btu/h-ft-degree F, in accordance with A6.1.
We trust that this will help you with your process and we thank you for
your interest in LEED Rating Systems.
If you have any further questions, please feel free to contact us via
the GBCI contact page: http://www.gbci.org/contactus.
Regards,
<name redacted>
GBCI Technical Customer Service
Green Building Certification Institute
2101 L St. NW . Suite 500
Washington DC 20037
800.795.1746 . fax 202.828.5110
WWW.GBCI.ORG
The text above represents a staff opinion on a particular issue, and
does NOT set any precedent to be upheld during a LEED Certification
Review. For official rulings in advance of a LEED Certification review,
customers should utilize the formal inquiry process available in LEED
Online. Applications for LEED Certification will be thoroughly reviewed
based upon the LEED Rating Systems balloted & approved by USGBC Members,
applicable Addenda, USGBC-approved LEED Interpretations, and Project
Credit Interpretation Rulings (CIRs) administered by GBCI, as
applicable. Please note that certain inquiries submitted to USGBC are
forwarded to GBCI for reply, as appropriate."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110517/0431d23c/attachment.htm>
More information about the Bldg-sim
mailing list