[Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED points
Marcus Sheffer
sheffer at energyopportunities.com
Mon May 16 07:35:09 PDT 2011
Read the study for yourself - http://www.newbuildings.org/sites/default/files/Energy_Performance_of_LEED-NC_Buildings-Final_3-4-08b.pdf
Here is another study analyzing the same data - http://www.nrc-cnrc.gc.ca/obj/irc/doc/pubs/nrcc51142.pdf
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com
www.sevengroup.com
-----Original Message-----
From: Eurek, John S NWO [mailto:John.S.Eurek at usace.army.mil]
Sent: Monday, May 16, 2011 10:12 AM
To: Hussein Abaza; Marcus Sheffer
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED points
Here is a link discussing leed and the 50% of the buildings consume as much
energy as non Leed buildings.
http://www.youtube.com/watch?v=mvCP3s7Xq48
After seeing this video Henry Gifford became one of my new heros.
Green is the new Red.
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Hussein Abaza
Sent: Saturday, May 14, 2011 7:47 PM
To: sheffer at energyopportunities.com
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED
points
There is a famous study ( I don't recall the link to it) which shows that
almost 50% of LEED buildings consume as much and more energy than non LEED
buildings.
----- Original Message -----
From: "Marcus Sheffer" <sheffer at energyopportunities.com>
To: "Julia Beabout" <juliabeabout at yahoo.com>, "Nick Caton"
<ncaton at smithboucher.com>, "Hussein Abaza" <ahussein at spsu.edu>, "Bill Bishop"
<wbishop at pathfinder-ea.com>
Cc: bldg-sim at lists.onebuilding.org
Sent: Saturday, May 14, 2011 4:36:22 PM GMT -05:00 US/Canada Eastern
Subject: RE: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED
points
The primary purpose is to get the conversation started, early. It is an
opportunity to educate the owner and the team about energy. In my experience
the majority of designers can’t even tell you the metric for comparing
building energy consumption. I have often had this conversation early in the
project design and have been met with blank stares. It is incumbent upon us
who do understand these energy issues to get the conversation started.
Caveat the heck out of the goal, explain the limitations, discuss the
relative vs absolute metrics, be open about the issues – so that we can raise
awareness one conversation at a time. This is the power of a market
transformation tool like LEED. It enables us to have these conversations.
I agree that both of these items are potential issues, talk to your clients
about them. If you don’t have a goal, how do you measure success?
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com <mailto:sheffer at sevengroup.com>
www.sevengroup.com
From: Julia Beabout [mailto:juliabeabout at yahoo.com]
Sent: Saturday, May 14, 2011 9:57 AM
To: Marcus Sheffer; Nick Caton; Hussein Abaza; Bill Bishop
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED
points
While I conceptually agree with and understand the kbtu or watts/sf approach,
to me, there seems to be some series issues with it in reality.
First, I don't agree that generating or coming up with appropriate target
values during design is always (or even frequently) an easy thing to do or
easy data to find. It depends on your bldg type. I do a lot of labs and
hospitals. Manufacturing and industrial use bldgs can have the same issues.
Good EUI data is not easy to come by for these bldg types - partly because
the user equipment that is installed in them can be a big portion of the
energy demand and consumption and it's always changing and can be very
specific to each client. For example: is it a community hosptial with more
modest and generic care provide?....a state of the art hospital with
specialized care functions?....does the lab have primarily biology or a
chemistry functions....etc etc. These things all affect the EUI. In my
opinion, the best resource for this data is actually utility companies based
on data from similar customers, but that data is not generally publicly
available and/or the population of similar comparable buildings may be small
and difficult to relate to your bldg.
Second, quite frankly, in my opinion, DESIGN phase energy models are poor
predictors of ACTUAL bldg energy use. They are best at predicting RELATIVE
(comparative) energy use. This is not because the tools are not good or
inaccurate but because we and the owners are so poor at predicting how the
bldg will actually be used, weather, etc. One additional factor, is what
equipment will actually be installed. It's not uncommon for the technology
to have changed bewteen the time that we start design and the time the
equipment is actually purchased closer to the end of construction. All these
things effect not only the equipment w/sf usage but the ac w/sf usage etc.
So, there seems to me to be a serious disconnect to me if we talking about
setting energy targets during DESIGNbased on statistical data of ACTUAL
energy use and trying to use those figure during the design phase for
predicted energy use. Again, I love the idea but are we really there yet in
reality. It seems to me we need a lot more data that doesn't exist yet - and
mechanism to collect that data. (CBECS etc are good, but the population and
variability for bldgs of these types has a long way to go).
I missing something about what's being proposed/talked about?
________________________________
From: Marcus Sheffer <sheffer at energyopportunities.com>
To: Nick Caton <ncaton at smithboucher.com>; Hussein Abaza <ahussein at spsu.edu>;
Bill Bishop <wbishop at pathfinder-ea.com>
Cc: bldg-sim at lists.onebuilding.org
Sent: Fri, May 13, 2011 7:01:25 PM
Subject: Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED
points
First of all the goal is not at all arbitrary but must be based on an
expected outcome within a reasonable expectation. It is informed by data
from similar, actual building energy consumption. I don’t think I need to
explain the tools one can use to do this.
Your goal (do the best you can) sounds like, “let’s build an energy efficient
building”. This is meaningless. Energy efficiency in the context of new
construction is always relative and without a quantification of what energy
efficient means this is no goal at all.
Like any early stage performance goal the number is adjustable as more is
discovered in the design process. If the target is later discovered to be
unreasonable due to a wide range of potential issues, then the target is
adjusted.
If you pick your EUI goal the way you describe then yes this is a worthless
goal but the key point is that it is never selected arbitrarily.
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com <mailto:sheffer at sevengroup.com>
www.sevengroup.com
From: Nick Caton [mailto:ncaton at smithboucher.com]
Sent: Friday, May 13, 2011 6:17 PM
To: Marcus Sheffer; Hussein Abaza; Bill Bishop
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED
points
Not to be a jerk, but to ask an honest question: what is the point? I’ve
been involved with “established energy target” projects and never really
picked up on the logic behind it – I would appreciate a layman’s explanation.
Put another way: If you select an arbitrary EUI or watts per square foot at
the earliest stages of design, what have you gained in design process?
If/when a project “meets the goal” mid-design, are future design decisions
supposed to de-emphasize energy impact (no!)? If on the other hand, a
project finds that target unreasonable down the road, what then?
Not setting a mile-marker like this implies designing the best building you
can given the time/budget available and any other constraints… that seems
more likely to result in the best end-result to me.
To draw analogy, if design of a LEED (or any energy-conscious) project is
like planning a road trip from Kansas to Florida, setting EUI goals seems
something like choosing a rest stop by throwing a dart at the map
blindfolded. It doesn’t help you get to your destination any more
efficiently, it may be far out of the way, and now you’ve got a hole in the
wall… what was the point?
Okay, maybe a weak analogy – chalking it up to a very long week =).
Honestly, I’d appreciate someone laying the value behind this approach – I’m
expect the logic does exist, and I just haven’t yet seen the light!
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Marcus Sheffer
Sent: Friday, May 13, 2011 4:36 PM
To: 'Hussein Abaza'; Bill Bishop
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Energy Model Cost - best design doesn'tequalmost LEED
points
Agreed. The new credit language for the next version of LEED does ask
project teams to establish an absolute performance goal.
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com <mailto:sheffer at sevengroup.com>
www.sevengroup.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Hussein Abaza
Sent: Friday, May 13, 2011 10:15 AM
To: Bill Bishop
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Energy Model Cost - best design doesn't equalmost
LEED points
Could any one advice why LEED would not put the base design as Watt per
square foot, or per occupant, or per hotel bed etc. so the Architecture
becomes more innovative early in the design to save energy?
----- Original Message -----
From: "Bill Bishop" <wbishop at pathfinder-ea.com>
To: "Arpan Bakshi" <arpanbakshi at gmail.com>
Cc: bldg-sim at lists.onebuilding.org
Sent: Friday, May 13, 2011 10:11:30 AM GMT -05:00 US/Canada Eastern
Subject: Re: [Bldg-sim] Energy Model Cost - best design doesn't equal most
LEED points
Arpan,
Based on the Weidt Group paper, I’m guessing you’re emphasizing architectural
considerations that affect the energy cost vs. LEED points numbers. (The
paper uses window-to-wall ratios and daylighting as an example.) I would
think the goal during the programming and schematic design phases should be
energy cost, not LEED points relative to the App. G baseline. Much of the
energy cost savings vs. App. G baseline (EAc1 points) is going to come later
from the mechanical and lighting designs. The suggestions in the paper to
establish specific baseline building shapes and glazing percentages would add
a LOT more modeling time – you’d have to create two separate building
geometries for the baseline and proposed models, not to mention different
zoning patterns, space types, lighting power per space etc.
For mechanical design, once the size and programming of the project is
established, the baseline model properties are pretty well set, unless you
consider fuel-switching and go between baseline systems 1/3/5/7 to systems
2/4/6/8. One exception I can think of for a design decision that results in
higher energy cost but better comparison with the App. G baseline is higher
ventilation rates combined with heat recovery in the proposed and no heat
recovery in the baseline.
Regards,
Bill
Signature in jpg form
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Arpan Bakshi
Sent: Friday, May 13, 2011 9:09 AM
To: sheffer at energyopportunities.com
Cc: <bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Energy Model Cost
Marcus, thank you incorporating this language.
The one scenario we often see in our design guidance work is that a proposed
design when compared with other design alternates does not necessarily
provided the largest energy savings when compared against its own baseline
case model. It is difficult to make a recommendation as consultants when we
want to present the Owner with both real energy cost savings without
compromising their LEED certification level targets.
A recent paper presented by the Weidt Group at SimBuild touched on this
issue:
http://www.ibpsa.us/pub/simbuild2010/technicalPresentations/SB10-PPT-TS02A-03
-Baker.pdf
Arpan Bakshi, LEED AP BD+C
YRG sustainability
On May 13, 2011, at 8:16 AM, "Marcus Sheffer"
<sheffer at energyopportunities.com> wrote:
If anyone has any good ideas about how to structure the LEED credits
to end the practice of validation models at the end and encourage/require
design phase modeling the folks on the USGBC EA TAG would love to hear them.
The current proposed credit language from the first public comment phase is
listed below.
NC, CS, SCHOOLS, RETAIL, WAREHOUSE & DISTRIBUTION CENTERS,
HOSPITALITY
Establish an energy performance target no later than the schematic
design phase. The target must be established as kBTU per square foot-year of
source energy use. This target must be mapped on the same scale as the
baseline and proposed buildings, if the project follows Option 1.
OPTION 1. Whole Building Energy Simulation
Analyze a minimum of at least nine efficiency measures during the
design process and account for the results in design decision-making.
Analysis can include energy simulation of efficiency opportunities,
application of past energy simulation analyses for similar projects to the
project, or application of published data from energy analyses performed for
similar projects to the project (such as AEDGs).
A minimum of six energy efficiency measures focused on load reduction
strategies appropriate for the facility must be analyzed. This analysis must
be performed during the schematic design phase.
A minimum of three energy efficiency measures focused on HVAC related
strategies must be analyzed (passive measures are acceptable). This analysis
must be performed before the conclusion of the design development phase.
The results of the analysis must be summarized in a brief report or
memorandum.
The next version of LEED will be going out for public comment again
in July, I think, so please comment formally as well as discussing here.
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com <mailto:sheffer at sevengroup.com>
www.sevengroup.com
From: John Aulbach [mailto:jra_sac at yahoo.com]
Sent: Thursday, May 12, 2011 7:46 PM
To: Carol Gardner; Marcus Sheffer
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Energy Model Cost
OK, Carol..now you threw the "bait" out there..older than dirt, eh?
I have done very limited LEED "type" modeling where you compare 20
walls and 40 windows types (well, it seemed that way). Correct me if I am
wrong, but a Base model must be built to comply with a certain level of
ASHRAE 90.1 (now up to 2010 ??). With all of the nuisances of eQuest 3.64, I
am going to build the model from scrathc and put in all the relevant baseline
data in by hand. And, by the way, the ASHRAE baseline model might be an
entirely different system. I am just completing an EPACT evaluation (ASHRAE
90.1-2001) and the Baseline HVAC was screwe chillers, whereas the Actual
building was packaged units with Turbocor compressors (ask me how I did
that).
It very much depends on the complexity of the building. A 40,000 sf
office or a 500,000 sf hotel with casino facilites.
I am unfamiliar with the LEED paperwork to be filled out after the
modeling has been done. But I would not do anything of this type in under 120
hours, preferably 160 hours. If the client thinks he can do better, let him.
Contingency, contingency.
We won't discuss how old CAROL might be..
John A.
________________________________
From: Carol Gardner <cmg750 at gmail.com>
To: sheffer at energyopportunities.com
Cc: bldg-sim at lists.onebuilding.org
Sent: Thu, May 12, 2011 2:59:12 PM
Subject: Re: [Bldg-sim] Energy Model Cost
Marcus,
You have inadvertently hit upon why IBPSA worked with ASHRAE to
create a BEMP certification. That's Building Energy Modeling Professional
(BEMP).
Some of us who have been in the field for awhile began to worry a
couple of years ago when so many new energy modelers began appearing on the
listserv with questions. Their questions indicated a lack of training and
experience that was worrisome. What made it worrisome was that they didn't
seem to realize that they were as inexperienced as they were; they didn't
appear to be pursuing training to learn how to do what they were doing; and
we were uncertain as to how or if they were practicing quality control. We
hoped that by creating a path to certification that we would give clients one
more qualification to look for in their modelers.
If you have been in this industry for any length of time, and by
industry I mean the overall construction industry, you know that you don't
get a lot of chances if your work doesn't pan out. If your energy model says
I have a LEED Gold building and I'm going to save $4,000/year and what I
really get is LEED Silver and $1,000/year, I am not going to be happy. So, I
will probably not give you any more work but, even worse for all of us, I'll
start expressing doubts about the whole process. LEED - what is it good for?
So, now we all have more training, right? We read our ASHRAE
Handbooks and technical manuals so we know how to model the difficult stuff.
We can find any topic in the DOE2 Manuals, all of which are one line,
available, and easily searchable.
So now we are so good we can do these models in 40-80 hours. Really?
Not me and I've been doing it longer than everyone, except you, John Aulbach.
So I'm going to join Marcus in his rant because he's on to something.
It's up to us to not under bid this work. It's up to us to educate
our clients about the importance of quality in this process. If they think
they are getting the same analysis in 40 hours that they used to get in 120
hours, they need to be led around to rethinking that and to be reminded that
GIGO.
Cheers,
Carol
Thu, May 12, 2011 at 2:31 PM, Marcus Sheffer
<sheffer at energyopportunities.com> wrote:
In our experience a final model, done right, would take about
80 hours.
WARNING – frustrated modeling rant to follow:
Doing just a final model however completely misses the point
as to why we model – it is to guide design decisions!
If I saw this RFP and all it asked me for was a model to
determine LEED points, during or after design, I would try to educate the
potential client about the purpose of modeling.
Unfortunately too many projects pursuing LEED are only doing
the minimum when it comes to modeling and almost completely missing all the
benefits. Too often the “market” transforms only based on a least first cost
denominator basis that results in little real transformation. Doing models
to determine LEED points does not transform the market, save any energy, and
just circumvents the purpose behind LEED. (the next version actually requires
design phase modeling!)
Any “modeler” who does only final models without attempting
to explain to the owner why this is a bad idea should be “drummed out of the
corp” in my humble opinion.
The problem is that if you respond to this RFP with 120 or
160 or more hours to really do the design phase modeling right, you will go
up against the “modeler” who claims to be able to do it in far less time. So
how do we get the folks who issue the RFPs to ask for a proper scope of work
so that they can compare fees on a level playing field? It is unfortunate
that we are even having a discussion about doing modeling work in opposition
to its purpose.
Sorry for the rant but I feel better now. J
Marcus Sheffer
Energy Opportunities, Inc/a 7group Company
1200 E Camping Area Road, Wellsville, PA 17365
717-292-2636, sheffer at sevengroup.com
<mailto:sheffer at sevengroup.com>
www.sevengroup.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Demba Ndiaye
Sent: Thursday, May 12, 2011 4:28 PM
To: Omar Delgado; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Energy Model Cost
Omar,
I would expect, for a building this size, approximately 40
hours (multiply by your hourly rate). The 40 hours include EAp2/EAc1 LEED
documentation, and any review you may have to respond to later.
Now, given that you have never done a LEED model, it will
take you more time, possibly up to 40 more hours.
HTH,
_______________
Demba NDIAYE
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Omar Delgado
Sent: Thursday, May 12, 2011 7:08 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Energy Model Cost
Greetings everyone,
I have a question regarding the cost of an energy model for a
LEED project. Every energy model I've done so far has been for
existing buildings, mainly for optimization purposes.
However, I received an RFP to model a five-story, 41,500 sq. ft. building
that's currently on the design phase and is pursuing the
LEED-NC Silver certification. I really have no idea what would be a fair
price for this model since I'm going to have to use Appendix
G (ASHRAE 90.1) to evaluate the difference between the base
and proposed buildings. I don't know how much extra effort
this will take. I know the procedure, just haven't done it before.
Can you shed any light on this issue?
Thanks in advance!
Omar A. Delgado Colón, P.E., MEnvM., LEED AP BD&C
Vice President
EnerMech
PMB 340
130 Winston Churchill Ave.
San Juan, PR 00926-6018
Cel. (787) 224-6537
odelgado at enermechpr.com
info at enermechpr.com
www.enermechpr.com <http://www.enermechpr.com/>
<image001.gif> Please consider your environmental
responsibility before printing this e-mail
This Email is covered by the Electronics Communications
Privacy Act, 18 U.S.C. Sections 2510-2521 and is legally priviliged. The
information in this email is personal and confidential and is intended solely
for the addressee(s). Access to this email by anyone else is unauthorized. If
you are not an intended recipient, you must not read, use or disseminate the
information contained in the email. Any views expressed in this message are
those of the individual sender and may be subject to Attorney/Client
privilege and/or Work Product. You are hereby notified that any
dissemination, distribution or copying of this communications is strictly
prohibited.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message
to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________ Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org To
unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--
Dr. Hussein Abaza, Assistant Professor
Construction Management Department
SCHOOL OF ARCHITECTURE’
CIVIL ENGINEERING TECHNOLOGY
And CONSTRUCTION
1100 South Marietta Parkway, Marietta, GA 30060-2896
Website: www.spsu.edu/cost Tel: 678-915-3719 Fax: 678-915-4966
E-mail: ahussein at spsu.edu
--
Dr. Hussein Abaza, Assistant Professor
Construction Management Department
SCHOOL OF ARCHITECTURE’
CIVIL ENGINEERING TECHNOLOGY
And CONSTRUCTION
1100 South Marietta Parkway, Marietta, GA 30060-2896
Website: www.spsu.edu/cost <http://www.spsu.edu/cost> Tel: 678-915-3719
Fax: 678-915-4966
E-mail: ahussein at spsu.edu
More information about the Bldg-sim
mailing list