[Bldg-sim] PTHP Baseline outperforming VAV
Cheney
chenyu73 at gmail.com
Mon May 23 18:55:27 PDT 2011
Hi Marcus,
Also pay attention to better glass in the proposed design. In a
cooling-dominated building, better window means the heat can not easily
escape from the building. You will not easily get credit from improving your
window here.
Regards,
Cheney
LinkedIN @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b
On Mon, May 23, 2011 at 3:18 PM, James V Dirkes II, PE <
jim at buildingperformanceteam.com> wrote:
> Dear Marcus,
>
> · It seems that your Baseline system, at >5 floors, should be VAV
> with a chiller instead of a heat pump (using LEED 2009).
>
> · As modeled, your baseline DOES have a notably higher COP, so it
> may well use less energy. *Part load performance* will have a significant
> effect, so you may want to check and compare those curves.
>
> · Also check pump delta T and total pressure drop. If you
> continue with a non-chiller system, pump energy is a significant factor.
> If your Baseline becomes a chiller system, pump energy will probably become
> similar.
>
> · Check fan total pressure drop for each system since your fan
> power is significantly larger in the Proposed system.
>
> · In the US, it is common to apply occupancy sensors on a LEED
> project and ASHRAE 90.1 allows a 10% power reduction when these are used.
> You are not taking advantage of that and may want to do so.
>
>
>
> *The Building Performance Team
> **James V. Dirkes II, P.E., BEMP , LEED AP
> *1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Marcus
> *Sent:* Monday, May 23, 2011 4:24 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] PTHP Baseline outperforming VAV
>
>
>
> Hi all,
>
> Having some difficulty in an App. G model for a 6-floor 14,000 m2 GFA Hotel
> in zone 1B (Abu Dhabi). Assuming standard design for each, should a proposed
> VAV system out-perform window AC units (the baseline)?
>
> Proposed:
> VAV with 2 Air-cooled centrifugal chillers, chiller COP = 3.1 (2.8 if
> condenser fan energy included)
> Envelope - Better windows decrease heating demand by 8% rest of envelope is
> minimum required for compliance
>
> Baseline:
> System Packaged terminal heat pump, COP = 3.52
>
> Using Energyplus v6.0 the results are;
>
> Site Energy in End Uses BL Proposed COP5
> MWh MWh MWh
> Space Cooling 747.5 1052.0 715.6
> Heat Rejection 0.0 0.0 0.0
> Space Heating 1.3 0.1 0.1
> Pumps 0.0 60.0 60.0
> Fans - Interior 42.2 137.7 137.7
> Fans - Car park 0.0 0.0 0.0
> Interior Lighting 530.5 530.5 530.5
> Exterior Lighting 0.0 0.0 0.0
> Service Water Heating 0.0 0.0 0.0
> Receptacle/Process Equipment 146.3 146.3 146.3
> Data Centre Equipment 0.0 0.0 0.0
> Elevators and Escalators 0.0 0.0 0.0
> Total Site Energy 1467.9 1926.6 1590.2
>
> I have the energy for the baseline, the proposed with COP = 3.1, and then
> trying COP = 5. It seems that even if we drastically increase the COP of the
> chiller plant in the proposed VAV system, we still can't get any energy
> savings. Is this realistic, an artifact of the simulation, or just an error
> on my part?
>
> Any guidance would be appreciated,
>
> Marcus
> --
> Marcus Jones, LEED AP, M.Sc.
> *Freelance energy consultant*
> *Vienna, Austria*
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>