[Bldg-sim] Walk-in Coolers/Freezers
Haider Khan
haidermkhan at ymail.com
Fri May 27 19:44:29 PDT 2011
I have successfully modeled walk-in freezers for the upcoming Title 24 supermarket refrigeration code in E+. I used the explicit method which requires compressor racks. If you are using compressor rack objects make sure that you are choosing the right compressor and that the compressors can meet the load. The .err file will give a warning if the system cannot meet the refrigeration loads.
FYI, The dataset folder in the E+ folder has several compressor curves.
Haider.
Sent from my mobile device.
On May 23, 2011, at 10:19 PM, <kcreamer at nc.rr.com> wrote:
> Hi all,
>
> Is it possible to use EnergyPlus to model a walk-in cooler or freezer? I have tried but regardless of the temperature setpoint I choose for the freezer, the modeled temperature does not want to drop below about 42 F.
>
> Also, has anyone made a model of a cooler that accurately estimates electricity loads? I was able to model a cooler with a 45 F setpoint but I was way under the electricity consumption estimates I found for coolers/freezers on the web. I think my problem was the large amount of electrical usage for non-compressor loads – defrost cycle, evaporator fan, condenser fan, etc.
>
> Kurt Creamer
> Apex, NC
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110527/3b16cc72/attachment-0001.htm>
More information about the Bldg-sim
mailing list