[Bldg-sim] Low Ambient Strategy questioned in LEED Review
Carol Gardner
gems at spiritone.com
Thu Nov 17 01:36:34 PST 2011
tb,
After, you have read through this couple of times, or looked at it in
an Excel table, you will figure out the changes you have to make and
make them. Always remember, do the proposed case first and then back out
the baseline, which must meet the applicable code.
I think in a case like this building you would have had a different
result if you had attached, or put into the form, what you were trying
to do and how you did it. Your explanation is quite good and it gives
the reviewers something to look at besides numbers. Then you get to
exercise both sides of your brain.
Cheers,
Carol
On 11/16/2011 10:26 PM, Tom Butler wrote:
>
> Sorry for the long attachment here, but this LEED v2.2 EAc1 comment
> has me really confused so I want to post it in its entirety.
>
> 1.The EAc1 Narrative describes the interior lighting design target for
> all studio spaces is 20 fc and that task lights have been modeled
> identically in the Baseline and Proposed case. However, according to
> the IESNA Lighting Handbook, ninth edition, the minimum horizontal
> design illuminance for art studios is 50 fc and for reading areas with
> handwritten tasks is 30 fc. The ASHRAE allowances represent the power
> allowance required to meet the minimum IESNA illuminance requirements
> for various space types. It is inappropriate to claim savings for
> designs that do not meet the minimum lighting level requirements and
> model the additional lighting power in the Baseline for lighting in
> the Proposed that is required to perform the anticipated tasks.
>
> Also, Table 1.4 reports that 4.02 kW of process lighting has been
> modeled in both cases, and it is assumed that this represents the task
> lighting. Process lighting is limited to the exempt interior lighting
> applications described in Section 9.2.2.3. Task lighting is regulated
> and thus not considered a process load. Section 9.6.3(b) does provide
> an additional allowance for task lighting when the Space by Space
> Method is used, but this may not be used for lighting required to
> raise the ambient lighting to meet the required lighting levels. If
> this additional allowance is used in the Proposed design, the Baseline
> must be modeled with the same power as the Proposed up to the 0.35
> W/square foot allowance. Please remove all task lighting power from
> the Baseline model that is required to meet the IESNA recommended
> illuminance levels. If any of the additional allowance from Section
> 9.2.2.3 is applied to the Baseline case, provide calculations
> verifying that this additional lighting is not required in the
> Proposed case to meet the required illuminance levels and confirming
> that this only represents the portion of the additional allowance that
> is used in the Proposed case.
>
> My first question; isn't low ambient-task specific a commonly accepted
> energy use reduction strategy? Why would I model a lighting design in
> the proposed solution which isn't installed and how would one
> determine, without an extensive lighting design effort, the
> appropriate lighting power to achieve 50fc, or 30fc? (not quite sure
> which one they want)
>
> Second, the spaces in question are architecture college studios. If
> the task lighting is a plug in desk lamp, provided by the student,
> then am I correct in assuming it's not regulated by 9.2.2.3? I've
> assumed 60W per lamp as plug load, but there no way that the lamp type
> or light distribution can be controlled as defined in 9.6.3.b, nor is
> it a given that a lamp will be used.
>
> I'm at a loss as to how to respond to this.
>
> Thanks for any input.
>
> tb
>
> *Tom Butler*
>
> *Residential Green Building Services Project Manager*
>
> *Tel: 404-604-3635*
>
> *Fax: 404-872-5009*
> *Email: **tbutler at southface.org* <mailto:amcfarland at southface.org>
>
> *Web: **www.southface.org* <http://www.southface.org/>**
>
> 241 Pine Street NE, Atlanta, GA 30308
>
> Description: sf logo without tag <http://www.greenprints.org/>
>
> *Building know-how for a sustainable future*
>
> **
>
> cid:image016.png at 01CC251F.C8476DC0
> <http://twitter.com/#%21/southfaceenergy>cid:image017.png at 01CC251F.C8476DC0
> <http://www.linkedin.com/company/southface>cid:image018.png at 01CC251F.C8476DC0
> <http://www.facebook.com/southface.energy>cid:image019.png at 01CC251F.C8476DC0
> <http://www.youtube.com/southfaceenergy>**
>
> **
>
> **
>
> */Get involved with /**Southface*
> <http://www.southface.org/get-involved/become-a-member/>*/today!/*
>
> cid:image003.jpg at 01CB96C8.7598B9C0
> <http://www.twitter.com/southfaceenergy>//cid:image004.jpg at 01CB96C8.7598B9C0
> <http://www.linkedin.com/companies/southface>//cid:image005.jpg at 01CB96C8.7598B9C0
> <http://www.facebook.com/pages/Southface/92291631957>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1630 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0008.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1200 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1246 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1016 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 1538 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 785 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0009.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 839 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0010.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 821 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111117/9fb2b978/attachment-0011.jpeg>
More information about the Bldg-sim
mailing list