[Bldg-sim] LEED Kitchen/Laundry HVAC Systems
Jorge Torres Coto
jorgembo1 at gmail.com
Fri Nov 25 09:36:08 PST 2011
I worked on the LEED for Retail, mostly the EA section and there is verbiage
in there for "process loads", utilizing alternative calculation methods
http://www.usgbc.org/ShowFile.aspx?DocumentID=7956
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Reba Schaber
Sent: Monday, November 21, 2011 7:07 PM
To: Rob Hudson; Fred Betz
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] LEED Kitchen/Laundry HVAC Systems
I don't have anything from USGBC, but I have some history from ASHRAE.
There are a series of interpretation requests to ASHRAE 90.1 about how
handle AC systems serving primarily process loads. It is clear that ASHRAE
considers AC systems serving primarily process loads exempt from
requirements of ASHRAE 90.1. Since they don't have to meet minimum
efficiencies, they need to be modeled the same when demonstrating compliance
with ASHRAE 90.1. See interpretation 4 about a theoretical central plant
that is used mainly for IT cooling.
"The central plant is exempt from the requirements of Standard 90.1 and
should be identical in both the Proposed Building Design and Budget Building
Design."
The interpretation is worded for Chapter 11, which is another means to show
compliance to the standard. However it is interesting to note they are no
longer applying this interpretation to Appendix G of 90.1-2007. This seems
like a logical progression sense Appendix G is meant to show energy
efficiency not compliance.
"This interpretation also applies to Section 11 of 90.1-2007 as well as
Appendix G of 90.1-2004 but does not apply to Appendix G of 90.1-2007."
Perhaps that knowledge may be helpful.
~Reba
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Thursday, October 27, 2011 1:58 PM
To: Fred Betz
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] LEED Kitchen/Laundry HVAC Systems
I completely agree with you Fred. This is the same logic that i followed.
Unfortunately my superiors do not agree with this logic, even though I have
shown them the same exception that you mention. Their logic states that
process loads shall be the same in both models, and anything associated with
process loads (such as cooling for a data room or exhaust/make up air for a
kitchen) do not serve any purpose except for process and therefore is also
process.
Does anyone have anything from USGBC clarifying this issue? I have looked
through the interpretations and nothing speaks to the HVAC equipment of
process loads.
Thanks for the input so far,
Rob
On Thu, Oct 27, 2011 at 4:51 PM, Fred Betz <fbetz at aeieng.com> wrote:
HVAC energy consumption caused by process loads cannot be called process
loads. Nor would you want it to be a process load, because then you can't
take credit for savings or at least not as easily.
Correct, your electrical or IT room with 90kW baseline is a system 3, and
your Proposed can be an efficient design. ASHRAE 90.1-2007 G3.1.1 exception
b allows you to apply system 3 for zones with large process loads.
This can be a huge source of energy savings. Enjoy it now, because rumor has
it that the next version of 90.1 will set an alternate baseline for IT rooms
and the like, and system 3 will no longer be applicable because the energy
savings can be ridiculously large.
Fred Betz PhD., LEED AP
Sustainable Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1175 | F: 608.238.2614
<mailto:fbetz at aeieng.com> fbetz at aeieng.com | <http://www.aeieng.com/>
www.aeieng.com
From: Rob Hudson [mailto:rdh4176 at gmail.com]
Sent: Thursday, October 27, 2011 12:54 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED Kitchen/Laundry HVAC Systems
In the situation that a design is utilizing an efficient exhaust/make up air
system, the LEED book says that an exceptional calculation may be used to
help quantify savings. This leads me to believe that the kitchen cooking
equipment is process, but the HVAC equipment is not. My office has been
having a "discussion" about whether HVAC equipment that conditions air for
process equipment is considered process as well.
Another example that is plaguing me: an electrical rack room has 90 kW of
stuff and requires 25 tons of cooling. If i use an efficient design, can i
take credit for it by comparing my design to a baseline of system 3 (PTAC w/
DX cooling and furnace heating)? I believe that this HVAC system should be
allowed to get credit, but others argue that because it serves process
equipment, then it is "process" heating/cooling.
Any thoughts from LEED AP out there? (i'm still working on getting my LEED
AP).
Thanks,
--
Rob Hudson
--
Rob Hudson
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1834 / Virus Database: 2092/4578 - Release Date: 10/27/11
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111125/1a383087/attachment-0001.htm>
More information about the Bldg-sim
mailing list