[Bldg-sim] ASHRAE 90.1 2007 Baseline System Selection
Otto Schwieterman
oschwieterman at fhai.com
Tue Oct 4 05:58:35 PDT 2011
Thanks Bill,
I think you are right. I will have to use exception "a" from G3.1.1 in
order to use system 5. The academic portion of the building has a VRF
system with the outside air conditioned by hot water from a natural gas
condensing boiler. I am going to separate the spaces that have outside
air (classrooms, offices, corridors......) and spaces that has no direct
outside air (restrooms, technology rooms.....) in the model so I can use
system 5 and 6 if the areas that are conditioned with only electric is
over 20,000 SF. This should work because the spaces that have outside
are conditioned with natural gas/electric and many of the other areas
are conditioned with only electric.
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Sent: Tuesday, October 04, 2011 8:41 AM
To: Otto Schwieterman; Cheney
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] ASHRAE 90.1 2007 Baseline System Selection
Otto,
My interpretation is that you determine your baseline system first
"based on usage, number of floors, conditioned floor area and heating
source", unless G3.1.1 exception a. applies. If, for example, your
school has 20,500 ft2 of classrooms with electric heating and the rest
of the school is gas, you could justify using both System 5 and System
6, instead of applying System 7 to the whole school. The note to Table
G3.1.1A only mentions exception a., so I don't think you can subtract
areas from other exceptions to G3.1.1 from the baseline system type
determination. If you're hoping to use System 5, carefully double-check
the conditioned floor area.
Regards,
Bill
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Tuesday, October 04, 2011 7:34 AM
To: Cheney
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 2007 Baseline System Selection
Thanks Cheney.
Has anyone attempted to do this on a LEED project? Did the reviewer
accept this and were there any comments?
From: Cheney [mailto:chenyu73 at gmail.com]
Sent: Monday, October 03, 2011 7:59 PM
To: Otto Schwieterman
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 2007 Baseline System Selection
Hi Otto,
As per 90.1-2007 Addendum W, " Where attributes make a building eligible
for more than one baseline system type, use the predominant condition to
determine the system type for the entire building except as noted in
Exception a to Section G3.1.1." Since your lab < 20,000ft2, my
understanding is that you can use system 5.
Regards,
Cheney
LinkedIN @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b
<http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b>
On Mon, Oct 3, 2011 at 2:30 PM, Otto Schwieterman <
oschwieterman at fhai.com> wrote:
I am modeling a school that is 150,700 SF. There is a welding lab in the
school and it falls within the exceptions of ASHRAE 90.1 2007: G3.1.1
Exception b. ("Peak thermal loads that differ by 10 btuh/sf or more from
the average of the other spaces served by the system..."). The welding
lab is 3,500 SF and I would use System 3 (PSZ-AC) for this space.
When I refer to Table G3.1.1A, one of the notes reads "Where attributes
make a building eligible for more than one baseline system type, use the
predominant condition to determine the system type for the entire
building." Does this allow me to use System 5 (Packaged VAV with Reheat)
instead of System 7 (VAV with Reheat) since the predominant condition
serves 147,200 SF (150,700-3,500)?
This is a LEED project and I would obviously rather use system 5 than
system 7 as my baseline HVAC system.
Thanks,
Otto
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity. If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity. If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance.
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity. If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful. Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111004/b3504bbb/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111004/b3504bbb/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list