[Bldg-sim] EPACT - more questions
Nick Caton
ncaton at smithboucher.com
Tue Oct 4 07:16:17 PDT 2011
Hi Josh!
I took this as a sign that I need to freshen up on the recent legislation/clarifications... I found the 20% reference, but I'm finding something a bit more nuanced than a blanket 20%:
Ref: IRS Notice 2008-40 (http://www.irs.gov/irb/2008-14_IRB/ar12.html), Section 7:
.01 Energy Savings Percentages. A taxpayer may apply section 2.05 of Notice 2006-52 by substituting "10" for "162/3" in section 2.05(1) of such notice. If a taxpayer makes this substitution, the taxpayer must apply sections 2.03 and 2.04 of Notice 2006-52 by substituting "20" for "162/3" in sections 2.03(1)(a) and 2.04(1) of such notice. If § 179D is extended beyond December 31, 2008 [insert: it was, until December 31, 2013, by the same legislation introducing the TARP], the Internal Revenue Service and the Treasury Department expect, in the absence of other changes to § 179D, that the substitute percentages set forth in this section will be the only percentages used in determining whether property placed in service after December 31, 2008, is partially qualifying property.
Having gone back and revised my copy of 2006-52 per the above, my interpretation is that improvements put into service after 2008 need to demonstrate a 20% improvement for lighting and/or HVAC, but only 10% for envelopes.
Partially qualifying installations put into service after December 31, 2008 have to submit for deductions using the 20/20/10 benchmarks. Anything prior has the option of submitting under either set.
That said, is there more recent legislation or an IRS "clarification" (haha) that mandates 20% for envelopes as well?
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Josh Howes
Sent: Monday, October 03, 2011 3:47 PM
To: bldg-sim at lists.onebuilding.org; R B
Subject: Re: [Bldg-sim] EPACT - more questions
Rohini,
We specialize in EPACT studies. The IRS legislation is very complicated and vague. However, to answer your questions:
1) Nick is correct. If you cannot get to 50% with your model by combining all the improvements (HVAC, lighting, and envelope), then you must model them separately. Remember, your baseline is not the building prior to the improvements. Your baseline is an ASHRAE 90.1-2001 baseline.
2) You are looking for 20% improvement on building improvements placed into service in 2008 or later. The 16 2/3% benchmark is only for years 2006 and 2007.
3) Nick is again correct.
We would be happy to work with you on future EPACT studies. Best of luck.
--------
Joshua D. Howes, PE
Concord Energy Strategies
(502) 384-9078
www.concordenergystrategies.com
IRS Circular 230 Disclosure
To ensure compliance with requirements imposed by the IRS, we inform you that any U.S. federal tax advice contained in this document is not intended or written to be used, and cannot be used, for the purpose of (i) avoiding penalties under the Internal Revenue Code, or (ii) promoting, marketing, or recommending to another party any transaction or matter that is contained in this document.
From: "Nick Caton" <ncaton at smithboucher.com>
Subject: Re: [Bldg-sim] EPACT - more questions
Date: October 3, 2011 1:29:06 PM EDT
To: "R B" <slv3sat at gmail.com>, <bldg-sim at lists.onebuilding.org>
Hi Rohini,
I haven't actually put together a final set of documentation for the modeling approaches, but having scoured the legislation & IRS clarification docs at one, here's my current understanding:
1. "Running the proposed with both these systems as upgrades gives me ~40% cost savings." ß This means the whole building approach is out (<50%). You have to model the lighting/HVAC/envelope improvements independently ("partially qualifying").
2. For each independently modeled component (lighting/HVAC/envelope) that pushes savings past the 16-2/3% improvement mark, you get to claim $0.60/SF for the deduction.
3. The improved HVAC run will not benefit from any lighting/envelope improvements for these partially qualifying runs, and so on.
Not sure I recall a 20% improvement figure as part of the requirements, but I haven't brushed up on the particulars in a good while.
~Nick
<image001.jpg>
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com <x-msg://225/www.smithboucher.com>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of R B
Sent: Monday, October 03, 2011 11:48 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] EPACT - more questions
The building that I am working on will have upgrades to lighting and HVAC. Running the proposed with both these systems as upgrades gives me ~40% cost savings. This is more than the 40% that is needed (for lighting and HVAC individually 20%). My question is if this is partially qualifying (less than 50%), then should I run lighting and HVAC separately? and each should be 20% saving? In this case the benefit of lower lighting will not be available to HVAC.
Thanks
-Rohini
_______________________________________________
Bldg-sim mailing list
Bldg-sim at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111004/8564877d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111004/8564877d/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list