[Bldg-sim] LEED EAC1 Exceptional calcs - heating consumption
Cheney
chenyu73 at gmail.com
Wed Oct 5 09:07:13 PDT 2011
Well, my understanding is that exceptional calculation is used to document
meansres that may not be adequately modelled in a simulaiton program. Some
examples are lab exhaust system, appliance efficiencies in high-rise
residential building, etc. How do you define your hard-wired lighting
calculation from this point of view?
Remodeling with reduded LPD is necessary provided your hard-wired lighting
reduction affects internal heat gain and you would expect more heating
energy in this manner. I guess it is what the reviewer expect to see unless
you can prove him/her that your reduction will not trigger heating/cooling
energy variation.
Regards,
Cheney
LinkedIN @ http://ca.linkedin.com/pub/yu-cheney-chen/27/637/72b
On Wed, Oct 5, 2011 at 7:03 AM, Nick Caton <ncaton at smithboucher.com> wrote:
> I think something is missing in the story here…****
>
> ** **
>
> A reduction of lighting consumption is claimed to reduce heating
> consumption?****
>
> ** **
>
> As you say, lights are an internal heat source to some extent… reducing the
> lighting energy consumed by a significant fraction should cause a relative
> increase in heating and a reduction of cooling energies, right? I’m going
> to assume the reviewer’s vocabulary is simply flipped around and this is the
> point they were trying to make: Changing lighting should affect
> heating/cooling consumptions.****
>
> ** **
>
> As to how you document this – It would seem simplest if you simply worked
> your “exceptionally calculated” reduction back into the model. From your
> description I don’t know exactly what your “hard-wiring” strategy is that’s
> chopping off 40%, but applying a factor to the space LPD’s may be a decent
> approach. You could then demonstrate before/after results showing
> lighting/heating/cooling consumptions moving about by setting up a
> parametric run and using those reports.****
>
> ** **
>
> ~Nick****
>
> ** **
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER****
>
> ** **
>
> Smith & Boucher Engineers****
>
> 25501 west valley parkway, suite 200****
>
> olathe, ks 66061****
>
> direct 913.344.0036****
>
> fax 913.345.0617****
>
> www.smithboucher.com* *****
>
> ** **
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Ashraf Khan
> *Sent:* Wednesday, October 05, 2011 8:03 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] LEED EAC1 Exceptional calcs - heating consumption***
> *
>
> ** **
>
> I have performed Exceptional calculations in EAC1 credit for internal
> hard-wired lighting. I achieved savings up to 40%. ****
>
> ** **
>
> In Preliminary review, I received below comment ****
>
> ** **
>
> *“It is does not appear as if the reduction in heating consumption was
> considered. Address the reduction in space heating and ensure the
> consumption is appropriately reduced, and provide a revised template and
> updated energy model output summaries reflecting the changes.”*
>
> ** **
>
> ** **
>
> As light generates heating, so leed reviewer is requesting to provide the
> heating consumption calculations and to achieve more savings as it directly
> impact on cooling, even though calculations performed exceptionally.****
>
> ** **
>
> Could you please guide how to perform these heating consumption
> calculations and how to incorporate in energy model and Template with
> reference?****
>
> ** **
>
> Thanks,****
>
> Ashraf Khan****
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111005/55e0efbc/attachment-0002.htm>
More information about the Bldg-sim
mailing list