[Bldg-sim] LEED Baseline system definition

Javier Duran javier at b-green.cl
Thu Oct 13 04:32:21 PDT 2011


i agree with that, in this case biomass is consider renewable, but in can't
be offset from energy cost
thaks a lot for all your coments

-- 
Javier Durán Palma
Gerente General B-green SA


2011/10/12 Christopher Schaffner <chris at greenengineer.com>

> A basic principle of Appendix G is that fuel switching is not an energy
> efficiency strategy, and shouldn't get rewarded. So the LEED interpretations
> say that both baseline and proposed should use the same fuel with the same
> rate structure, whether it is oil, gas, coal or biomass. However, depending
> on the type and source of the biomass fuel, it may be considered "renewable"
> for LEED. If it qualifies as a renewable energy source, the energy cost
> becomes zero in the proposed case, and significant savings might be realized
> under EAc1.
>
> Check the LEED reference guide for the types of biomass that qualify as
> renewable. Generally speaking it has to be agricultural waste, and must be
> locally sourced.
>
> --
>
> Chris Schaffner, PE
> LEED Fellow
> Founder and Principal
>
> The Green Engineer, LLP
> Sustainable Design Consulting
> 50 Beharrell Street
> Concord, MA 01742
> T: 978.369.8978
> M:978.844.1464
> chris at greenengineer.com
> www.greenengineer.com
>
> The Green Engineer, LLP is a Certified B Corporation
>
>
>
> From: Javier Duran <javier at b-green.cl>
> Date: Wed, 12 Oct 2011 18:44:57 -0300
> To: Nick Caton <ncaton at smithboucher.com>
> Cc: <bldg-sim at lists.onebuilding.org>
> Subject: Re: [Bldg-sim] LEED Baseline system definition
>
> Hi everyone
>
> During last week greenbuild at toronto i met a reviewer i and ask her what
> kind of baseline system should i have when using biomass as heating fuel in
> the proposed system.
> She give me a different 'view': i should consider using biomass in both
> buildings, so i could only take advantage of the energy efficiency of the
> bioler (furnace) in the proposed, then i should consider the most used
> system's efficiency  in the zone.
> what do you think?, still confusing for me!
>
>
> --
> Javier Durán Palma
> Gerente General B-green SA
>
>
>
>
>
> 2011/9/1 Javier Duran <javier at b-green.cl>
>
>> Hi Nick
>> Thanks for the point, i think i will ask them before submitting, I´ll come
>> back with the answer.
>>
>>
>>
>> --
>> Javier Durán Palma
>> Gerente General B-green SA
>>
>>
>> 2011/9/1 Nick Caton <ncaton at smithboucher.com>
>>
>>> Hi Javier,****
>>>
>>> ** **
>>>
>>> I would arrive at the same conclusion based on a strict reading of 90.1.
>>> ****
>>>
>>> ** **
>>>
>>> I can’t speak directly for USGBC or its reviewership, but I would expect
>>> a rational/logical individual who is permitted to review models in a
>>> rational/logical fashion to at least consider accepting an alternate,
>>> non-electric baseline system *if* you can make a strong case for why a
>>> specific non-electric baseline would make for a fundamentally *better*
>>> system upon which to found a performance rating.  Perhaps circumstances
>>> specific to the region of Chile you’re working in mean an equivalent
>>> electric heating source would be infeasible?  I don’t personally believe
>>> 90.1 & LEED are at their core trying to make it inordinately easy *or*
>>> difficult for any specific region or circumstance, but rather trying to make
>>> the procedure as evenhanded as possible. ****
>>>
>>> ** **
>>>
>>> Before taking any action (other than pursuing an “electric or other”
>>> baseline system), I would first suggest determining whether you can make
>>> such a case.  If so, take the actions necessary to pose your situation/query
>>> in a written fashion to the correct parties through the proper LEED channels
>>> – It’s been said your LEED project administrator may have an email for
>>> directing project-specific questions to the appropriate parties outside of a
>>> formal CIR.  ****
>>>
>>> ** **
>>>
>>> ~Nick****
>>>
>>> [image: cid:489575314 at 22072009-0ABB]**
>>>
>>> * *
>>>
>>> *NICK CATON, P.E.***
>>>
>>> SENIOR ENGINEER****
>>>
>>> ** **
>>>
>>> Smith & Boucher Engineers****
>>>
>>> 25501 west valley parkway, suite 200****
>>>
>>> olathe, ks 66061****
>>>
>>> direct 913.344.0036****
>>>
>>> fax 913.345.0617****
>>>
>>> www.smithboucher.com* *****
>>>
>>> ** **
>>>
>>> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
>>> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Javier Duran
>>> *Sent:* Wednesday, August 31, 2011 7:10 AM
>>> *To:* bldg-sim at lists.onebuilding.org
>>> *Subject:* [Bldg-sim] LEED Baseline system definition****
>>>
>>> ** **
>>>
>>> Hi Everyone,****
>>>
>>> ** **
>>>
>>> We are working on LEED certification for a school project in the south of
>>> Chile. ****
>>>
>>> The building has a wood pellet based biomass Boiler to provide heating.
>>> Since the definition of the baseline system depends on the heating system of
>>> the proposed building, I am wondering how to clasified the wood pellet
>>> boiler.****
>>>
>>> The choices are:****
>>>
>>> 1    fossil fuel, ****
>>>
>>> 2    electric or Other****
>>>
>>> Should I consider wood pellet as " Other " and therefore the baseline
>>> system would be Electric?****
>>>
>>> ** **
>>>
>>> Many Thanks,****
>>>
>>> ** **
>>>
>>> --
>>> Javier Durán Palma****
>>>
>>> Gerente General B-green SA****
>>>
>>> ** **
>>>
>>> ** **
>>>
>>
>>
>>
>>
>>
>
>
>
>
> _______________________________________________ Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org To
> unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111013/a31001e7/attachment-0002.htm>


More information about the Bldg-sim mailing list