[Bldg-sim] LEED Baseline system definition
Javier Duran
javier at b-green.cl
Thu Sep 1 12:12:07 PDT 2011
Hi Nick
Thanks for the point, i think i will ask them before submitting, I´ll come
back with the answer.
--
Javier Durán Palma
Gerente General B-green SA
2011/9/1 Nick Caton <ncaton at smithboucher.com>
> Hi Javier,****
>
> ** **
>
> I would arrive at the same conclusion based on a strict reading of 90.1.**
> **
>
> ** **
>
> I can’t speak directly for USGBC or its reviewership, but I would expect a
> rational/logical individual who is permitted to review models in a
> rational/logical fashion to at least consider accepting an alternate,
> non-electric baseline system *if* you can make a strong case for why a
> specific non-electric baseline would make for a fundamentally *better*
> system upon which to found a performance rating. Perhaps circumstances
> specific to the region of Chile you’re working in mean an equivalent
> electric heating source would be infeasible? I don’t personally believe
> 90.1 & LEED are at their core trying to make it inordinately easy *or*
> difficult for any specific region or circumstance, but rather trying to make
> the procedure as evenhanded as possible. ****
>
> ** **
>
> Before taking any action (other than pursuing an “electric or other”
> baseline system), I would first suggest determining whether you can make
> such a case. If so, take the actions necessary to pose your situation/query
> in a written fashion to the correct parties through the proper LEED channels
> – It’s been said your LEED project administrator may have an email for
> directing project-specific questions to the appropriate parties outside of a
> formal CIR. ****
>
> ** **
>
> ~Nick****
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, P.E.***
>
> SENIOR ENGINEER****
>
> ** **
>
> Smith & Boucher Engineers****
>
> 25501 west valley parkway, suite 200****
>
> olathe, ks 66061****
>
> direct 913.344.0036****
>
> fax 913.345.0617****
>
> www.smithboucher.com* *****
>
> ** **
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Javier Duran
> *Sent:* Wednesday, August 31, 2011 7:10 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] LEED Baseline system definition****
>
> ** **
>
> Hi Everyone,****
>
> ** **
>
> We are working on LEED certification for a school project in the south of
> Chile. ****
>
> The building has a wood pellet based biomass Boiler to provide heating.
> Since the definition of the baseline system depends on the heating system of
> the proposed building, I am wondering how to clasified the wood pellet
> boiler.****
>
> The choices are:****
>
> 1 fossil fuel, ****
>
> 2 electric or Other****
>
> Should I consider wood pellet as " Other " and therefore the baseline
> system would be Electric?****
>
> ** **
>
> Many Thanks,****
>
> ** **
>
> --
> Javier Durán Palma****
>
> Gerente General B-green SA****
>
> ** **
>
> ** **
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110901/37bb0005/attachment-0002.htm>
More information about the Bldg-sim
mailing list