[Bldg-sim] exterior convection coefficient for tilted roof
Jeff Haberl
jhaberl at tamu.edu
Sat Feb 11 13:55:59 PST 2012
Leen,
This depends on whether or not the wind is blowing... or not. ASHRAE used to have tabluated values (still in some textbooks) of R = .17 Btu/ft2-hr-F for winter (15 mph wind) and .25 Btu/ft2-hr-F for summer (7 mph wind). Otherwise, for a vertical surface it would be .68 for free convection, probably less for a tilted surface, .9 if horizontal heat flow down.
Also, radiation can be significant if the surface is facing a cloudless sky. I think Kreider's solar textbook has a equation for sky temperature...which is somewhat complicated by cloud cover, etc.
Jeff
8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=)8=?
Jeff S. Haberl, Ph.D.,P.E., FASHRAE..............jhaberl at tamu.edu
Professor............................................................Office Ph: 979-845-6507
Department of Architecture.............................Lab Ph:979-845-6065
Energy Systems Laboratory.............................FAX: 979-862-2457
Texas A&M University.....................................77843-3581
College Station, Texas, USA, 77843..................URL:www.esl.tamu.edu
8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=)8=0
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [bldg-sim-bounces at lists.onebuilding.org] on behalf of leen peeters [l.f.r.peeters at gmail.com]
Sent: Saturday, February 11, 2012 1:59 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] exterior convection coefficient for tilted roof
Dear,
can anyone point me to some reference values for exterior convection coefficients for tilted surfaces like a roof?
Thanks
Leen
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120211/54238ab8/attachment-0001.htm>
More information about the Bldg-sim
mailing list