Hayes Zirnhelt
hzirnhelt at hotmail.com
Mon Jan 2 14:58:57 PST 2012
Hi Leen,
I typically use the formula: ach (normal pressure) = ACH at 50Pa/20, based on Kronvall and Persily - this is known as the KP model.
A more detailed model for converting ACH at 50 can be found in Sherman 1987:
Estimation of Infiltration from Leakage and Climate Indicators
Energy and Buildings, 10 (1987) 81 - 86
If your modelling a passive house it may be worth using a more sophisticated model than the KP model. You can also look in the EnergyPlus Engineering Reference manual, it discusses some methods developed by DOE etc for IBlast and DOE-2 to modify the actual infiltration rate for wind and other factors on an hourly basis according to the weather file.
Regards,
Hayes
Hayes Zirnhelt
M.A.Sc Candidate, RU Building Science
B.A.Sc Integrated Engineering
hayes.zirnhelt at ryerson.ca
On 2012-01-02, at 1:30 PM, bldg-sim-request at lists.onebuilding.org wrote:
> Send Bldg-sim mailing list submissions to
> bldg-sim at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> bldg-sim-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> bldg-sim-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Bldg-sim digest..."
> Today's Topics:
>
> 1. infiltration rate passive building (leen peeters)
> 2. Air temperature stratification layer in EnergyPlus (Sachin Sharma)
> 3. Re: Radiant Floor Temperature in EnergyPlus (Sachin Sharma)
>
> From: leen peeters <l.f.r.peeters at gmail.com>
> Date: January 1, 2012 4:48:26 PM PST
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] infiltration rate passive building
>
>
> Dear all,
>
> what is the standard (not 50Pa) infiltration rate I should use as input to the TRNSYS type56 building model in case of simulating a passive house?
>
> thanks!
>
> Leen
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120102/e182bc78/attachment.htm>
More information about the Bldg-sim
mailing list