[Bldg-sim] [Equest-users] Lesson Learned: Single Zone Packaged DX vs. Packaged VAV system types
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Tue Jan 17 15:20:48 PST 2012
Kristy-
Did you try to use the "WASTE-HEAT-USE" feature of the PSZ system for humidity control?
[cid:image001.jpg at 01CCD544.BCBF0730]
I've had success using this feature to achieve the desired space humidity conditions with 100% OA units.
I can't remember whether its energy performance is appropriate, but I did verify with hourly reports that the zones in question had accurate humidity control.
I remember having a hard time finding this feature - several late nights with the DOE-2 dictionary - but I eventually found the documentation on Vol 2 - Dictionary - pp398-399 and pp416-417.
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Walson, Kristy
Sent: Tuesday, January 17, 2012 2:47 PM
To: 'equest-users at lists.onebuilding.org'
Subject: [Equest-users] Lesson Learned: Single Zone Packaged DX vs. Packaged VAV system types
Hi all,
I just wanted to share a lesson learned that I ran across recently while using Equest. Here are the pertinent specs for the building:
* Proposed Case
o 65,000 sq ft of laboratory (with ac/hr requirements)
o Cooling is provided by a chilled water district plant
o Heating is provided by a district steam boiler plant
o 100% outdoor air
o Humidity control is being utilized
* Baseline
o Per G3.1.1 Exception (c), baseline system type is #3, Packaged DX, Constant Volume, Fossil Fuel Furnace
o Humidity control is included because it's in the design case (ASHRAE 90.1-2007 Table G3.1 Part 1.b)
[cid:image005.jpg at 01CCD543.F9B33C20]
o 100% outdoor air, or a percentage to match the proposed
Because the ASHRAE baseline system was #3, I used the Equest system type "Packaged Single Zone" for the baseline model and then proceeded to pull my hair out for a day because the baseline model was performing better than the proposed. Then I decided to try changing the baseline system type to "Packaged VAV" and setting the fan control to "Constant" with the minimum flow ratio set to "1", in order to force it to still be a constant volume system. The first thing I noticed after only changing the system type was that the cooling energy almost doubled. The upshot is the following, for these Equest system types:
* Packaged Single Zone
o When you add reheat in order to control humidity, the software shows an increase for the heating energy, but does not show an increase in cooling energy. Cooling energy should also increase because it now has additional heat due to reheat to overcome. The place to verify humidity control is the SS-N report, which showed that humidity was not being controlled, despite the fact that I had set the maximum humidity to 60% in the inputs.
* Packaged VAV
o When you add reheat, the software shows an increase in both heating and cooling energy. This is correct. Otherwise, your baseline building will always perform better than the proposed. Again, verify that humidity is being controlled in the SS-N report.
LESSON LEARNED: Always use the Packaged VAV system type in Equest when modeling DX equipment. If you have a constant volume system, just adjust the fan control to be "Constant" and the minimum airflow ratio to be "1".
I hope this makes sense. Feel free to comment if you've had experience with this. Thanks!
Kristy M. Walson, PE, LEED AP BD+C, BEMP
Associate / Sustainability Consultant
TLC Engineering for Architecture
Your 2030 Challenge Partner
255 South Orange Avenue, Suite 1600
Orlando, FL 32801-3463
phone:
407-841-9050
fax:
407-425-7367
direct:
407-487-1118
website:
www.tlc-engineers.com<http://www.tlc-engineers.com>
[cid:image006.gif at 01CCD543.F9B33C20]<http://www.tlc-engineers.com/>
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120117/b72d301f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 49063 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120117/b72d301f/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.gif
Type: image/gif
Size: 5272 bytes
Desc: image006.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120117/b72d301f/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 17668 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120117/b72d301f/attachment-0001.jpg>
More information about the Bldg-sim
mailing list