[Bldg-sim] Calibrated Simulations & ASHRAE G14
David Eldridge
dse at grummanbutkus.com
Thu Jan 5 08:21:03 PST 2012
RE: [Bldg-sim] Calibrated Simulations & ASHRAE G14
There are probably occupancy variations that took place in the house that
cause variance in the energy usage for the measured case, and it may be
difficult for you to capture those effects in the model.
Other building occupancies (commercial, institutional, etc.) stick more
closely to their typical usage patterns and the benchmark CV should be
achievable in most cases.
It should be for residential also if you have enough data about the usage
to tailor the operating schedules.
You might want to start out with a gas usage and HDD regression to identify
if there are any months that jump out as atypical from your modeling,
irregular usage periods, etc.
DHW could be significant also, maybe you can get water usage data for the
house to see if there were periods when occpuants were using more
showers/sinks/laundry/etc.
One other idea might be to see how sensitive the CV is to the measured ACH,
which could vary during times of the year, not sure if your measurement
covered multiple data points (summer/winter/occpupied/unoccupied).
Hope this helps!
David
***
*
*****David S. Eldridge, Jr.******, P****.******E****.******, LEED AP BD+C,
BEMP, BEAP, HBDP*
Project Manager
Direct: (847) 316-9224 | Fax: (847) 328-4550
*****Grumman/Butkus Associates* | 820 Davis Street, Suite 300 | Evanston,
IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers
***
*
-----Original Message-----
From: *bldg-sim-bounces at lists.onebuilding.org*<bldg-sim-bounces at lists.onebuilding.org>
*[mailto:bldg-sim-bounces at lists.onebuilding.org]*<[mailto:bldg-sim-bounces at lists.onebuilding.org]>On
Behalf Of Hayes Zirnhelt
Sent: Wednesday, January 04, 2012 4:27 PM
To: *bldg-sim at lists.onebuilding.org* <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Calibrated Simulations & ASHRAE G14
Hi,
Does anyone have experience with calibrated simulations? Especially, in
accordance with ASHRAE guideline 14, or other standards / guidelines.
I've been working on a calibrating and EnergyPlus model to measured gas
HVAC data for a single family house with extensive monitoring and detailed
information available and I am finding it very difficult to achieve the <=
30% CV RSME that Guideline 14 suggests.
I'm surprised that it is this challenging because I have far more
information available than what would likely be available in typical
modelling jobs. Eg. ACH rating, measured ground temperature data, full
as-built plans, indoor temperature measurements....
So I'm curious to hear about anyone else's experiences with this. Is this
guideline generally achievable for modellers?
Thanks,
Hayes Zirnhelt
M.A.Sc Candidate, RU Building Science
B.A.Sc Integrated Engineering
*hayes.zirnhelt at ryerson.ca* <hayes.zirnhelt at ryerson.ca>
_______________________________________________
Bldg-sim mailing list
*http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org*<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
To unsubscribe from this mailing list send a blank message to *
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG* <BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120105/d7ffda98/attachment-0002.htm>
More information about the Bldg-sim
mailing list