[Bldg-sim] EE4 (DOE-2.1E) Water-Side Economizer Issue
Jake Martell
jmartell at mreng.ca
Tue Jul 24 10:35:31 PDT 2012
Hello,
-I am looking to simulate a water-side economizer in EE4 (DOE-2.1E) by
altering the .doe file.
-I have added the highlighted text below into the "Plant-Parameters" section
of the .doe file.
PLANT-PARAMETERS
BOILER-CONTROL = STANDBY
HW-BOILER-HIR = 1.0870
CHILLER-CONTROL = STANDBY
$ Cooling Tower $
TWR-SETPT-CTRL = FIXED
TWR-SETPT-T = 85.0
TWR-DESIGN-WETBULB = 73.0
TWR-DESIGN-APPROACH= 12.0
TWR-DESIGN-RANGE = 10.0
TWR-THROTTLE = 5
TWR-CAP-CTRL = ONE-SPEED-FAN
TWR-CELL-CTRL = MIN-CELLS
DIRECT-COOL-MODE = STRAINER-CYCLE
DC-MAX-OAT = 39.0
DC-MAX-CHILL-WTR-T = 44.0
DC-TWR-WTR-SETPT = 44.0
DIRECT-COOL-KW = 0.055
$ Condenser Water Pumps $
TWR-MOTOR-EFF = 0.917
TWR-IMPELLER-EFF = 0.790
TWR-PUMP-HEAD = 60.00
..
-After running the simulation and comparing it to previous results, there
are savings on "Space Cooling" but there is also a greater energy usage in
"Heat Reject" as show in the table below. The DOE-2 guide suggests entering
the condenser water pumping power as kW/ton but maybe I should be entering 0
for DIRECT-COOL-KW if I'm accounting for the condenser water pumps twice?
This is for a project in Nova Scotia so I think there should be savings from
turning off the chillers throughout the winter but it doesn't make sense
based on these results.
Energy Use Category
Before Change
After Change
Savings
(MBtu)
(MBtu)
(MBtu)
% Sav
Area Lights
2,252.2
2,252.2
0
0.0%
Misc. Equipment
1,629.1
1,629.1
0
0.0%
Space Heat
2,062.0
2,062.0
0
0.0%
Space Cool
615.6
475.7
140
22.7%
Heat Reject
121.5
295.6
-174
-143.3%
Pumps & Misc.
1,136.2
1,136.2
0
0.0%
Vent Fans
2,168.4
2,168.4
0
0.0%
DomHot Water
587.6
587.6
0
0.0%
TOTAL
10,572.6
10,606.8
-34
-0.3%
Best regards,
Jake R. Martell, EIT
Mechanical Engineer-in-Training
t: (902) 422-7393
f: (902) 423-4945
e: <mailto:jmartell at mreng.ca> jmartell at mreng.ca
The electronic message contained herein is private and confidential,
intended only for the recipient(s) specified. If you have received this
message in error, please delete it and notify us immediately. Any
accompanying files are supplied as a matter of courtesy only. The data are
without warranty of any kind. Any person or business making use of the data
is responsible for confirming its accuracy and completeness. M&R Engineering
Ltd. is not responsible for edited or produced versions of this digital
information.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120724/1d3479a0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1857 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120724/1d3479a0/attachment.jpeg>
More information about the Bldg-sim
mailing list