Jim Dirkes
jim at buildingperformanceteam.com
Wed Jul 18 08:58:59 PDT 2012
Te Qi,
If the file uses a NightCycle Availability Manager, E+ will operate the HVAC during unoccupied hours to maintain the applicable setpoint.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Te Qi
Sent: Wednesday, July 18, 2012 11:30 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Question about Energyplus
Hello everyone,
I am doing a case study about a office building in design builder(E+) using the compact system (VAV with reheat +outside air set). While I set the cooling setpoint schedule as only working during occupied hours(7-18), also I check the E+ file that the schedule I set is right. However, when I check the meter about the cooling coils consumption, I realizedthe cooling coil and fans are still working during unoccupied hours, which confused me a lot. Could someone experienced tell me the reason. Thanks so much.
Te Qi
Intern of EEB Hub