[Bldg-sim] indoor gains for passive house
CleanTech Analytics
jeremiah at cleantechanalytics.com
Sat Jul 28 21:13:32 PDT 2012
My bad- it is .6 ACH50
*Jeremiah D. Crossett*
*CleanTech Analytics*
*503-688-8951*
*www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
*
This document may contain valuable information proprietary to CleanTech
Analytics which is private and confidential. It may not be shared, copied,
stored or transmitted in any form without the prior written consent of
CleanTech Analytics
*
On Sat, Jul 28, 2012 at 9:12 PM, CleanTech Analytics <
jeremiah at cleantechanalytics.com> wrote:
> Leen,
> I think that the requirement is 15 kBtu/sqft/Y for heating & cooling- and
> .06 ACH50 maximum.
> Possibly you will find the attached spreadsheet useful, as well as the
> values pasted below (these are from a project that meet/exceed the standard)
>
> All the best-
>
> Specific Space Heat Demand: 4.63 kBTU/(ft²yr) Pressurization Test
> Result: 0.45 ACH50 Specific Primary Energy Demand
> (DHW, Heating, Cooling, Auxiliary and Household Electricity): 33.3
> kBTU/(ft²yr) Specific Primary Energy Demand
> (DHW, Heating and Auxiliary Electricity): 14.4 kBTU/(ft²yr) Specific
> Primary Energy Demand
> Energy Conservation by Solar Electricity: kBTU/(ft²yr) Heating Load:
> 4.73 BTU/(ft2hr) Frequency of Overheating: % Specific Useful
> Cooling Energy Demand: 0.24 kBTU/(ft²yr) Cooling Load: 2.29 BTU/(ft2
> hr)
>
>
>
> *Jeremiah D. Crossett*
> *CleanTech Analytics*
> *503-688-8951*
> *www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
>
>
> *
>
> This document may contain valuable information proprietary to CleanTech
> Analytics which is private and confidential. It may not be shared, copied,
> stored or transmitted in any form without the prior written consent of
> CleanTech Analytics
> *
>
>
>
> On Sat, Jul 28, 2012 at 2:20 PM, leen peeters <l.f.r.peeters at gmail.com>wrote:
>
>> Hi,
>>
>> where can I find the typical indoor gain profiles (appliances, lighting,
>> equipment) for passive houses?
>>
>> thanks,
>>
>> leen
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120728/0eb14d89/attachment-0002.htm>
More information about the Bldg-sim
mailing list