Would you say that Open studio is finally "ready" for real world projects?
I have been a fan, and have made effort to use it for years but just never
found it to work very well (looks great tho)
If Open studio has got the bugs out I am sure many users would jump on
board- so is it ready?
Best regards-
*Jeremiah D. Crossett*
*CleanTech Analytics*
*503-688-8951*
*www.cleantechanalytics.com* <http://www.cleantechanalytics.com>
*
This document may contain valuable information proprietary to CleanTech
Analytics which is private and confidential. It may not be shared, copied,
stored or transmitted in any form without the prior written consent of
CleanTech Analytics
*
On Thu, Jun 7, 2012 at 8:35 PM, Pavel Dybskiy <pdybskiy at gmail.com> wrote:
> Hi Rob,
>
> I have installed OpenStudio
> I tried to import one of e+ example files,
> SolarCollectorFlatPlateWater.idf.
> It looks like OpenStudio didn't recognize quite a few objects, e.g.
> IddObjectType: 'WaterHeater:Mixed'
> Please advise.
>
> Pavel
>
>
> On Thu, Jun 7, 2012 at 11:58 AM, Guglielmetti, Robert <
> Robert.Guglielmetti at nrel.gov> wrote:
>
>> I would humbly submit OpenStudio (openstudio.nrel.gov) as a tool for
>> diagramming these systems. The OpenStudio application has a visual HVAC
>> system design tab in the interface that has been engineered to allow idiots
>> like me to create ASHRAE standard system types, and customize from there as
>> needed. While the graphics may not be super sexy, they tell the story.
>> Further, after you've dragged and dropped your way to a functional and
>> valid HVAC system description, you not only have a series of graphics that
>> illustrate it, you also have underlying code describing this system in
>> OpenStudio-speak, as well as EnergyPlus-speak, ready for simulation.
>>
>> Rob Guglielmetti
>> NREL
>>
>> ________________________________________
>> From: bldg-sim-bounces at lists.onebuilding.org [
>> bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Pavel Dybskiy [
>> pdybskiy at gmail.com]
>> Sent: Thursday, June 07, 2012 9:27 AM
>> To: EnergyPlus_Support at yahoogroups.com; bldg-sim at lists.onebuilding.org
>> Subject: [Bldg-sim] Tools to draw HVAC diagrams
>>
>> Sorry for cross-posting,
>>
>> Does anyone use MS Visio for sketching HVAC diagrams?
>> Is it a good alternative to Ms Word, which is somehow tolerable for
>> simple diagrams, but gets really out of hands for bigger diagrams?
>> The shapes, which are included in Visio, are they helpful, meaningful,
>> give professional look?
>>
>> Somebody is using Excel (might be lacking flexibility when topology is
>> unknown).
>> Somebody is using Inkscape.
>> Any other thoughts
>> Thank you,
>>
>> Pavel Dybskiy
>>
>>
>> On Mon, Jun 4, 2012 at 6:53 PM, Jim Dirkes <
>> jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>>
>> wrote:
>>
>> No “tool” Pavel, just Excel with formatted cells and arrows – pretty
>> unsophisticated, but easier (I think) than learning Inkscape. I know of
>> others using Inkscape, however, and it looks like a very capable tool.
>>
>> The Building Performance Team
>> James V. Dirkes II, P.E., BEMP , LEED AP
>> 1631 Acacia Drive NW
>> Grand Rapids, MI 49504
>> 616 450 8653<tel:616%20450%208653>
>>
>> From: EnergyPlus_Support at yahoogroups.com<mailto:
>> EnergyPlus_Support at yahoogroups.com> [mailto:
>> EnergyPlus_Support at yahoogroups.com<mailto:
>> EnergyPlus_Support at yahoogroups.com>] On Behalf Of Pavel Dybskiy
>> Sent: Monday, June 04, 2012 6:18 PM
>> To: EnergyPlus_Support at yahoogroups.com<mailto:
>> EnergyPlus_Support at yahoogroups.com>
>> Subject: [EnergyPlus_Support] Tools to draw HVAC diagrams
>>
>>
>>
>> Hi Jim,
>> What tool do you use to draw your diagram?
>>
>> Dear List,
>> I'm wondering if you can share your thoughts on your favorite tool to
>> draft efficiently such diagrams.
>> Is there anything better than pencil and paper?
>>
>> Thanks,
>>
>> Paul
>>
>>
>> On Mon, Jun 4, 2012 at 2:10 PM, Jim Dirkes <
>> jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>>
>> wrote:
>> Dear Forum,
>> The schematic I have attached is a common boiler plant piping
>> configuration in my experience, using an individual constant speed pump for
>> each boiler, plus a variable speed distribution pump.
>> Officially it’s a “primary – secondary pumping loop”.
>> I cannot make the primary pumps shut off when the corresponding boiler is
>> inactive. Has anyone successfully modeled this configuration? Do you know
>> of an example file with this configuration?
>> Thanks in advance.
>>
>> [cid:image001.jpg at 01CD4283.651E5C90]
>> Making me think….
>> Why is it? We routinely use miracles of creativity and technology that
>> 50-100 years ago would be considered impossible or black magic … and also
>> assume that whole segments of society are incapable of helping themselves
>> or acting intelligently. Is it a self-fulfilling expectation?
>>
>>
>>
>>
>> --
>> Best Regards,
>>
>> Pavel Dybskiy
>> M.A.Sc<http://M.A.Sc>. Candidate, Department of Architectural Science
>> Faculty of Engineering, Architecture and Science, Ryerson University
>> E-mail: pdybskiy at ryerson.ca<mailto:pdybskiy at ryerson.ca>;
>> telephone: 647-984-4940<tel:647-984-4940>
>>
>> __._,_.___
>> Reply to sender<mailto:jim at buildingperformanceteam.com?subject=RE%3A%20%5BEnergyPlus_Support%5D%20Tools%20to%20draw%20HVAC%20diagrams>
>> | Reply to group<mailto:EnergyPlus_Support at yahoogroups.com?subject=RE%3A%20%5BEnergyPlus_Support%5D%20Tools%20to%20draw%20HVAC%20diagrams>
>> | Reply via web post<
>> http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJxdTJpdGhxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI1MTgzBHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTMzODg1MDQ0Mw--?act=reply&messageNum=25183>
>> | Start a New Topic<
>> http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJlNjFmbWgzBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTMzODg1MDQ0Mw--
>> >
>> Messages in this topic<
>> http://groups.yahoo.com/group/EnergyPlus_Support/message/25180;_ylc=X3oDMTM2N2p0bzFzBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI1MTgzBHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTMzODg1MDQ0MwR0cGNJZAMyNTE4MA-->
>> (3)
>> Recent Activity:
>>
>> * New Members<
>> http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmZWdwcGg3BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzMzg4NTA0NDM-?o=6>
>> 9
>>
>> Visit Your Group<
>> http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJldTVnMDZlBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTMzODg1MDQ0Mw--
>> >
>> Primary EnergyPlus support is found at:
>> http://energyplus.helpserve.com or send a message to
>> energyplus-support at gard.com<mailto:energyplus-support at gard.com>
>>
>> The primary EnergyPlus web site is found at:
>> http://www.energyplus.gov
>>
>> The group web site is:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>> Attachments are currently allowed but be mindful that not everyone has a
>> high speed connection. Limit attachments to small files.
>>
>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
>> Documentation link and press the "search" button.
>> <
>> http://groups.yahoo.com/;_ylc=X3oDMTJkOWI0ZXEwBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzM4ODUwNDQz
>> >
>> Switch to: Text-Only<mailto:
>> EnergyPlus_Support-traditional at yahoogroups.com?subject=Change+Delivery+Format:+Traditional>,
>> Daily Digest<mailto:EnergyPlus_Support-digest at yahoogroups.com?subject=Email+Delivery:+Digest>
>> • Unsubscribe<mailto:EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe>
>> • Terms of Use<http://docs.yahoo.com/info/terms/>
>> .
>>
>> __,_._,___
>>
>>
>>
>> --
>> Best
>> -p.d.
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>
>
>
> --
> Best
> -p.d.
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120607/b5ebf992/attachment-0002.htm>
More information about the Bldg-sim
mailing list