Javed is right - that discussion on [Equest-users] pretty much covered all angles of this topic - recommended reading! Following is an additional response I threw together for Robby/Kris that I think nails down some grey areas:
I may be reading the question differently, but I would add the space-by-space method is not a requirement. It's usually a good idea from a "I want to get more LEED points perspective," as the space-by-space approach often yields a higher allowable LPD overall, but one can choose to model the proposed and baseline either using the building area or space-by-space approach. Do not however mix your approaches between the models.
This point (being able to use either method to tally/model LPD) is pretty explicitly made in the same cited Table G3.1 section under the Baseline requirements.
If the lighting designer has calculated the installed LPD, nothing in the standard dictates the modeler must perform separate takeoffs ... but expect to shoulder blame if those calculations do not satisfy the reviewers. From personal experience, I advise against placing a heavy amount of trust in others' LPD calcs. Energy models are only ever as strong as the weakest inputs used to build them.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of javed iqbal
Sent: Monday, June 25, 2012 12:38 PM
To: Kris Raj
Cc: Bldg-sim
Subject: Re: [Bldg-sim] Appendex G LPD
Kris,
There was a detail discussion on the same issue few weeks before on eQuest forum. you can check the archives by following key word:
"Building area method ASHRAE 90.1"
Hope you will get all your doubts clear there!
Thanks!
On Mon, Jun 25, 2012 at 10:41 PM, Kris Raj <kris_raj at rocketmail.com<mailto:kris_raj at rocketmail.com>> wrote:
Robby, Thanks for your response. I did see that section. It just gets confusing because the same section seems to indicate that the baseline lighting power density can be based on whole building method. Also the LEED EAp2 1.4 template excel spreadsheet has entries to indicate weather the lighting is based on space-by-space or building area method.
thanks
raj
________________________________
From: Robby Oylear <robbyoylear at gmail.com<mailto:robbyoylear at gmail.com>>
To: Kris Raj <kris_raj at rocketmail.com<mailto:kris_raj at rocketmail.com>>
Cc: Bldg-sim <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>>
Sent: Monday, June 25, 2012 12:08 PM
Subject: Re: [Bldg-sim] Appendex G LPD
Kris,
Refer ASHRAE 90.1-2007 Appendix G Table G3.1 item 6 for the Proposed Building Performance.
Yes, you have to go through the lighting layout and calculate the power for each zone.
Robby Oylear, P.E., LEED AP
Mechanical Engineer
Senior Energy Analyst
D 206-788-4571
www.rushingco.com<http://www.rushingco.com/>
On Mon, Jun 25, 2012 at 6:24 AM, Kris Raj <kris_raj at rocketmail.com<mailto:kris_raj at rocketmail.com>> wrote:
hello,
Does anyone know if we can use building area method for lighting in the proposed case for a LEED App G simulation. We were just given the total wattage of the building from the lighting designer. Or would we have to go through the lighting layout and calculate the power for each zone.
thanks
raj
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Javed Iqbal, LEED AP, CEA
Energy Analyst
M:+919891020464
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120625/7e29e0c4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120625/7e29e0c4/attachment-0002.jpg>
More information about the Bldg-sim
mailing list