[Bldg-sim] Solar gains differences between Design Builder and IES VE....
Timothy Moore
timothy.moore at iesve.com
Mon Nov 26 11:27:40 PST 2012
David,
I would caution you not to be so quick to use the term "underestimate," which implies that you are certain that your test is set up correctly and that know the EnergyPlus calcs to be accurate. Furthermore, given the magnitude of the disparity you've described-which does not show up either in the published ASHRAE 140 tests comparing results for the VE and EnergyPlus or in the SimBuild paper from Cassie Waddell and Shruti Kaserekar that Javed Iqbal attached to his reply-there may be something significantly amiss in your comparison.
You need to ensure that you are consistent with your glazing properties and you may want to be running the "detailed solar calculations" in EnergyPlus and, likewise, linking the simulation to results from the SunCast module within the VE if you want a suitably consistent basis for the comparison. This will facilitate calculation of incident solar radiation on specific surfaces, etc.
While I'm not sure how this works in EnergyPlus, when you run simulations coupled to the SunCast module in the VE, you need to be cognizant of the relative placement of glazing in your "test cell," as low-angle direct-beam radiation striking an east window in the early morning, for example, can pass through the space and out the other side, in keeping with the location and solar transmission of glazing on the façades through which the solar gain is entering and exiting.
On a related note, whereas the paper from Waddell and Kaserekar attributes the calculation of interior inter-surface radiant exchanges to the SunCast module of the VE, this is actually a function of the ApacheSim engine used for all dynamic thermal simulations in the VE. SunCast determines which surface the solar gain will fall upon and what fraction of each surface is shaded from direct-beam radiation at any given time step, as well as how much of those surfaces are shaded from the cooling effects of the night sky; however, regardless of SunCast, the hot interior surface of a piece of glass having absorbed solar gain, for example, will always exchange radiant energy with any interior surfaces of lower temperature during the simulation run. Conversely, the cold interior surface of a window or exterior wall in winter will always act as a sink for radiant energy from warmer interior surfaces.
Finally, if you're interested in digging deeper into the comparison, I was told by researchers at the Technical University at Eindhoven in The Netherlands attending the last SimBuild conference that their current findings (yet to be published) show that the solar calculations in the VE are actually somewhat more accurate than those in other tools, including EnergyPlus and ESPr, particularly when passing through multiple glazed surfaces, cavities, or thermal zones. As it's not yet published and IES was not involved in this research, I'll leave it to TU Eindhoven to elaborate on what they tested, what they found, and whether or not they believe this to be of any significance. They may be willing to share some results in advance of publication.
Regards,
Timothy
[cid:image001.jpg at 01CBEDFA.628DACD0]<http://www.iesve.com/>
Timothy Moore
Senior Product Manager
Mobile: 415 810-2495
Office: 415 983-0603
Internal IP ext. 8549 and 8589
timothy.moore at iesve.com<mailto:timothy.moore at iesve.com>
www.iesve.com <http://www.iesve.com/>
**Design, Simulate + Innovate with the <Virtual Environment>**
Email Disclaimer<http://www.iesve.com/disclaimer.html>
On Fri, Nov 23, 2012 at 5:23 AM, David GARCIA-SANCHEZ <dgarciasanchez at greenaffair.com<mailto:dgarciasanchez at greenaffair.com>> wrote:
Dear group,
In our current projects we noticed a big difference when modeling solar gains between the software IES VE and Designbuilder (EnergyPlus). IES VE underestimate the values of solar gains, by almost 1 to 2 of difference than EnergyPlus,
So I just try to ask if someone of you are experienced the same difference and if you know the reasons of that big difference. We test a "cell-test" and we found also this underestimation of solar gains.
Thanks in advance,
David Garcia Sanchez
David GARCIA-SANCHEZ
greenaffair
Tel. +33 (0)1 46 03 80 10<tel:%2B33%20%280%291%2046%2003%2080%2010>
Mobile +33 (0)6 78 15 08 09<tel:%2B33%20%280%296%2078%2015%2008%2009>
102 avenue Edouard Vaillant - 92100 Boulogne-Billancourt
www.greenaffair.com<http://www.greenaffair.com/>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Javed Iqbal, LEED AP, CEA
Energy Analyst
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20121126/51513305/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1668 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20121126/51513305/attachment-0002.jpg>
More information about the Bldg-sim
mailing list