[Bldg-sim] Modelling oil-fired systems with different COPs in Designbuilder (Simple HVAC)
Gupta, Apeksha
GuptaA at bre.co.uk
Fri Sep 14 02:17:54 PDT 2012
Hello All,
Thank you all very much for this interesting input. Made me realise what the 'Zone Heating' in Designbuilder suggests against the 'Heat generated' by the heating system.
Regards,
Apeksha
Apeksha Gupta
Renewable Energy KTP Associate, BRE Wales
Ethos, Kings Road, Swansea Waterfront, SA1 8AS
T +44 1792 630 109 M +44 (0) 754 894 3314 E Guptaa at bre.co.uk W www.bre.co.uk
MAP: http://tinyurl.com/brewales
Download the BRE Wales & South West brochure here
________________________________________
From: David Cocking [dave at arrow-energy-solutions.co.uk]
Sent: 13 September 2012 21:46
To: Gupta, Apeksha; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Modelling oil-fired systems with different COPs in Designbuilder (Simple HVAC)
Hi Apeksha,
I think you're saying the same thing in a different way. The heating demand of the building is met by the zone emitters (after any contributions from internal and external gains), and you wouldn’t expect the zone heating values to change with variations in boiler efficiency. The heat output from the heating plant is that required to meet the heating load; it is unaffected by efficiency but the amount of fuel consumed meeting that output will clearly vary with efficiency.
Hope that helps,
Dave
David Cocking
Director I M: 07939 353791 I E: dave at arrow-energy-solutions.co.uk
Arrow Energy Solutions Ltd I 1 Sundorne Avenue I Shrewsbury I SY1 4JW
T: 0870 0427264 I F: 0870 8381398 I www.arrow-energy-solutions.co.uk
Do you need to print this? Be green, read on screen.
Privileged/Confidential information and/or Copyright Material may be contained in this email. The information and material is intended for the use of the addressee(s) only. If you are not the addressee or the person responsible for delivering it to the intended addressee(s), you may not copy or deliver it to anyone else or use it in any unauthorised manner. To do so is prohibited and may be unlawful. If you receive this email by mistake, please advise the sender immediately by replying to the email. Although this email and attachments are believed to be free of any virus or other defects which might affect any computer or IT systems into which they are received, no responsibility is accepted by Arrow Energy Solutions Ltd for any loss or damage arising in any way from the receipt or use thereof.
Arrow Energy Solutions Ltd Registered in England & Wales, Company Registration No. 6402543. Standard terms and conditions apply.
-----Original Message-----
From: Gupta, Apeksha [mailto:GuptaA at bre.co.uk]
Sent: 13 September 2012 09:51
To: David Cocking; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Modelling oil-fired systems with different COPs in Designbuilder (Simple HVAC)
Hi David,
Zone heating is in fact the heating demand of the building that is unaffected by the plant's efficiency as pointed out by Jim Dirkes. When I looked at the heat generation results they were varying for different efficiencies with all other parameters remaining equal.
Thanks,
Apeksha
Apeksha Gupta
Renewable Energy KTP Associate, BRE Wales Ethos, Kings Road, Swansea Waterfront, SA1 8AS
T +44 1792 630 109 M +44 (0) 754 894 3314 E Guptaa at bre.co.uk W www.bre.co.uk
MAP: http://tinyurl.com/brewales
Download the BRE Wales & South West brochure here ________________________________________
From: David Cocking [dave at arrow-energy-solutions.co.uk]
Sent: 12 September 2012 19:22
To: Gupta, Apeksha; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Modelling oil-fired systems with different COPs in Designbuilder (Simple HVAC)
Apeksha,
It might just be a case of misinterpreting the results...I would advise checking the “simulation detailed results” descriptions in the help file. The zone heating is the heat input to the zone from the zone emitters, not the energy consumed by the plant. You should find that your energy consumption at building level changes with a change in plant efficiency (providing all else remains equal).
Hope that helps,
Dave
David Cocking
Director I M: 07939 353791 I E: dave at arrow-energy-solutions.co.uk<mailto:dave at arrow-energy-solutions.co.uk>
Arrow Energy Solutions Ltd I 1 Sundorne Avenue I Shrewsbury I SY1 4JW
T: 0870 0427264 I F: 0870 8381398 I www.arrow-energy-solutions.co.uk<http://www.arrow-energy-solutions.co.uk/>
P Do you need to print this? Be green, read on screen.
Privileged/Confidential information and/or Copyright Material may be contained in this email. The information and material is intended for the use of the addressee(s) only. If you are not the addressee or the person responsible for delivering it to the intended addressee(s), you may not copy or deliver it to anyone else or use it in any unauthorised manner. To do so is prohibited and may be unlawful. If you receive this email by mistake, please advise the sender immediately by replying to the email. Although this email and attachments are believed to be free of any virus or other defects which might affect any computer or IT systems into which they are received, no responsibility is accepted by Arrow Energy Solutions Ltd for any loss or damage arising in any way from the receipt or use thereof.
Arrow Energy Solutions Ltd Registered in England & Wales, Company Registration No. 6402543. Standard terms and conditions apply.
From: Gupta, Apeksha [mailto:GuptaA at bre.co.uk]
Sent: 11 September 2012 14:35
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Modelling oil-fired systems with different COPs in Designbuilder (Simple HVAC)
Hello All,
I’m trying to compare two oil boilers with different COPs. One is 55% efficient and the other 82% efficient. I’m using the Simple HVAC model, however the results for Zone heating (kWh) do not change for the two boilers. All other parameters of the building remain the same. One would expect the lower efficiency boiler to perform more leading to a higher energy consumption to a higher efficiency boiler. Has anyone come across this in simulations? Can’t understand what I am doing incorrectly.
Regards,
Apeksha
Apeksha Gupta MSc
Renewable Energy KTP Associate
BRE Wales & South West
Ethos, Kings Road,
Swansea- SA1 8AS
T +44 1792 630 109 M +44 (0) 754 894 3314 E Guptaa at bre.co.uk<mailto:Guptaa at bre.co.uk> W www.bre.co.uk<http://www.bre.co.uk/>
MAP: http://tinyurl.com/brewales
________________________________
For Green Deal news, information and more details on becoming involved: visit the BRE Green Deal Website Here<www.bre.co.uk/greendeal>
Follow BRE on Twitter: @BREwatford<http://twitter.com/brewatford>
________________________________
Privileged and confidential information and/or copyright material may be contained in this e-mail. If you are not the intended addressee you may not copy or deliver it to anyone else or use it in any unauthorised manner. To do so is prohibited and may be unlawful. If you have received this e-mail by mistake, please advise the sender immediately by return e-mail and destroy all copies. Thank you.
Building Research Establishment Ltd, Registered under number 3319324 in England and Wales. VAT Registration No GB 689 9499 27 www.bre.co.uk<http://www.bre.co.uk>
BRE Global Limited, Registered under number 3548352 in England and Wales. www.breglobal.com<http://www.breglobal.com>
Building Research Establishment and BRE Global are subsidiaries of the BRE Trust.
BRE Trust is a company limited by guarantee, Registered under number 3282856 in England and Wales, and registered as a charity in England (no. 1092193) and in Scotland (no. SC039320). www.bretrust.org.uk<http://www.bretrust.org.uk>
Registered Offices: Bucknalls Lane, Garston, Watford, Hertfordshire WD25 9XX - Travelling to BRE: see www.bre.co.uk/directions<http://www.bre.co.uk/directions>
________________________________
------------------------------------------------------------------------------------------------------------------------------
The 40 Percent Symposium, 28 November, London: One-day, international sustainability conference, managing the implications of sustainability in the built environment: www.40percentsymposium.com
Follow BRE on Twitter: @BREwatford
------------------------------------------------------------------------------------------------------------------------------
Privileged and confidential information and/or copyright material may be contained in this e-mail.
If you are not the intended addressee you may not copy or deliver it to anyone else or use it in any unauthorised manner. To do so is prohibited and may be unlawful.
If you receive this e-mail by mistake, please advise the sender immediately by return e-mail and destroy all copies. Thank you.
Building Research Establishment Ltd, Registered under number 3319324 in England and Wales. VAT Registration No GB 689 9499 27. www.bre.co.uk BRE Global Limited, Registered under number 3548352 in England and Wales. www.breglobal.com Building Research Establishment and BRE Global are subsidiaries of the BRE Trust.
BRE Trust is a company limited by guarantee, Registered under number 3282856 in England and Wales, and registered as a charity in England (no. 1092193) and in Scotland (no. SC039320).
Registered Offices: Bucknalls Lane, Garston, Watford, Hertfordshire WD25 9XX - Travelling to BRE: see www.bre.co.uk/directions
------------------------------------------------------------------------------------------------------------------------------
------------------------------------------------------------------------------------------------------------------------------
The 40 Percent Symposium, 28 November, London: One-day, international sustainability conference,
managing the implications of sustainability in the built environment: www.40percentsymposium.com
Follow BRE on Twitter: @BREwatford
------------------------------------------------------------------------------------------------------------------------------
Privileged and confidential information and/or copyright material may be contained in this e-mail.
If you are not the intended addressee you may not copy or deliver it to anyone else or use it in any unauthorised
manner. To do so is prohibited and may be unlawful.
If you receive this e-mail by mistake, please advise the sender immediately by return e-mail and destroy all copies. Thank you.
Building Research Establishment Ltd, Registered under number 3319324 in England and Wales. VAT Registration No GB 689 9499 27. www.bre.co.uk
BRE Global Limited, Registered under number 3548352 in England and Wales. www.breglobal.com
Building Research Establishment and BRE Global are subsidiaries of the BRE Trust.
BRE Trust is a company limited by guarantee, Registered under number 3282856 in England and Wales, and registered
as a charity in England (no. 1092193) and in Scotland (no. SC039320).
Registered Offices: Bucknalls Lane, Garston, Watford, Hertfordshire WD25 9XX - Travelling to BRE: see www.bre.co.uk/directions
------------------------------------------------------------------------------------------------------------------------------
More information about the Bldg-sim
mailing list