[Bldg-sim] LEED Swimming Pool Sizing and ACH
Demba Ndiaye
Demba.Ndiaye at setty.com
Tue Sep 18 14:31:26 PDT 2012
Thanks Guys,
I appreciate your comments.
I use System 3 as recommended by Appendix G for pool space conditioning. Evaporation load is included. Relative humidity is maintained to max 60%. But still, the sizing I get for the Baseline remains below 4 ACH. I would like to find backup material to make the case that the Baseline should use 4 ACH as the Proposed. Equitable? Or maybe not?
Any more ideas?
Regards,
Demba.
From: Jim Dirkes [mailto:jim at buildingperformanceteam.com]
Sent: Tuesday, September 18, 2012 4:46 PM
To: Aaron Smith; Demba Ndiaye; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] LEED Swimming Pool Sizing and ACH
In a recent LEED project with a pool, my assumptions were:
* The Aquatics space requires special temperature and humidity for 24/7 schedule, and thus merits use of a "non-predominant" special Baseline (System #3 or #4)
* The Baseline system (#3 in this case) used the standard delta T, fan power, etc.
* The Proposed system used hot gas reheat, a standard (80%) efficiency boiler for additional heating, heat recovery for the minimum outdoor airflow, and heat recovery from hot gas (if available after reheating) for pool water heating
* Pool water heating, including pool wall conduction loads and pool pumps were considered "process" loads
* Results were favorable!
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: Aaron Smith [mailto:asmith at mreng.ca]
Sent: Tuesday, September 18, 2012 4:33 PM
To: Jim Dirkes; 'Demba Ndiaye'; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: RE: [Bldg-sim] LEED Swimming Pool Sizing and ACH
Demba,
In previous versions of LEED, I think you could consider the pool a process load and model the natatorium as an empty space. Now that you need to include process loads, perhaps you can have the reference and proposed equal unless you are trying to claim savings as Jim mentioned.
Aaron
Aaron Smith, P.Eng
LEED(r) AP BD+C, M-ASHRAE, Mechanical Engineer
[cid:image001.jpg at 01CD95C3.4743F610]
t: (902) 422-7393
f: (902) 423-4945
e: asmith at mreng.ca<mailto:asmith at mreng.ca>
The electronic message contained herein is private and confidential, intended only for the recipient(s) specified. If you have received this message in error, please delete it and notify us immediately. Any accompanying files are supplied as a matter of courtesy only. The data are without warranty of any kind. Any person or business making use of the data is responsible for confirming its accuracy and completeness. M&R Engineering Ltd. is not responsible for edited or produced versions of this digital information.
________________________________
From: Jim Dirkes [mailto:jim at buildingperformanceteam.com]<mailto:[mailto:jim at buildingperformanceteam.com]>
Sent: Tuesday, September 18, 2012 5:00 PM
To: Demba Ndiaye; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] LEED Swimming Pool Sizing and ACH
Dear Demba,
Airflow is only one of the comparisons for a pool. The others, all very powerful in impact, are de-humidification, and heat recovery from the refrigeration system for reheating and pool water heating, and heat recovery for outdoor air preheating.
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org]<mailto:[mailto:bldg-sim-bounces at lists.onebuilding.org]> On Behalf Of Demba Ndiaye
Sent: Tuesday, September 18, 2012 3:51 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] LEED Swimming Pool Sizing and ACH
ASHRAE Applications recommends a minimum of 4 ACH for natatoriums. Applying that minimum to my Proposed leads to a somewhat oversized pool unit compared to the Baseline system, which reduces my savings a lot. I couldn't find a code requirement of a minimum amount of ACH, which would allow me to size the Baseline with the same number of 4 ACH. Is somewhere aware of any such code requirement?
A related question: would LEED allow to size the Baseline at 4 ACH, even though the project is not a school?
Thanks for chime in,
[cid:image004.jpg at 01CD95C3.4743F610]Demba Ndiaye, Ph.D., P.E., LEED AP BD+C, BEMP
Energy Analyst/Mechanical Engineer
Setty & Associates, Ltd.
MEP Design Engineering | Project Management
|Construction Management | Design-Build Services | Commissioning
|3040 Williams Drive, Suite 600 | Fairfax, VA 22031
|Voice 703.691.2115 | Fax 703.691.8084 | cell 571.830.9913
demba.ndiaye at setty.com<mailto:demba.ndiaye at setty.com> | www.setty.com<http://www.setty.com/>
This e-mail and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. If you are NOT the intended recipient or the person responsible for delivering the e-mail to the intended recipient, be advised that you have received this e-mail in error and that any use, dissemination, forwarding, printing or copying this e-mail is strictly prohibited.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120918/1b2c39a1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1849 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120918/1b2c39a1/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 167 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120918/1b2c39a1/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 15865 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120918/1b2c39a1/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 2902 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120918/1b2c39a1/attachment-0008.jpg>
More information about the Bldg-sim
mailing list