You are correct, when BOILER-TYPE =
ELECTRIC-BOILER, the BOILER-EIR and BOILER-HIR
keywords have no bearing on what is reported in BEPS for heating.
Your best bet is to use a different version of
DOE2.1e (the EE4 version does not work
correctly), modify your EE4 generated .DOE file
to use HP-LOOP-HEATING = FROM-PLANT. Then you
can set the BOILER-EIR in Plant accordingly.
At 07:00 PM 27/09/2012, Marc-Antoine Paquin wrote:
>Content-type: multipart/related;
>boundary="Boundary_(ID_QS7ygEnFJj4JQkRFaCgNNA)"
>Content-language: fr-ca
>
>Hello all, we are simulating a VRF system with EE4.
>
>To do so, we used zonal heating pumps coupled to
>a cooling tower and an electric
>boiler. However, we want to modify the boiler
>EIR in order to simulate the condenser (HP) that
>is actually adding heat to the hot water
>loop. To do so, we changed the Elec-Boiler EIR
>in Doe2.1
unfortunately, this had no influence
>on the heating consumption. We verified if the
>boiler was used or not in the global annual consumption and it was.
>
>We tried the same for a 4-pipe system and the
>heating consumption did changed with the EIR modification.
>
>Does anyone have a clue of how to proceed to
>modify the boiler EIR while usinf zonal HP system.
>
>Regards,
>
>Marc-Antoine Paquin, ing.
>Directeur Service simulation
>
>SignatureCouriel
>
>
>________________________________
>Le présent courrier électronique (courriel) et
>les documents qui y sont attachés peuvent
>contenir de l'information confidentielle; ils
>s'adressent exclusivement au(x) destinataire(s)
>mentionné(s) ci-dessus et nulle autre personne
>ne doit en prendre connaissance ni les utiliser
>ou les divulguer. Si vous recevez le présent
>courriel par erreur, veuillez en aviser
>l'émetteur immédiatement par courrier
>électronique et le détruire avec les documents qui y sont attachés.
>The information contained in this e-mail and all
>attachments is confidential and is for the sole
>use of its intended recipient. It may not be
>disclosed to or used by anyone other than the
>addressee. If received in error, please contact
>the sender by return e-mail and delete this
>e-mail and all attachments from your system.
>
>De : bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] De la part de Chris
>Envoyé : 27 juin 2012 12:44
>À : Eleni Soulti
>Cc : equest-users at lists.onebuilding.org; bldg-sim at lists.onebuilding.org
>Objet : Re: [Bldg-sim] VRF system in eQUEST
>
>Try this...
>
>
>On Tue, Jun 26, 2012 at 11:25 PM, Eleni Soulti
><<mailto:elenisoulti at co2engineering.eu>elenisoulti at co2engineering.eu> wrote:
>Dear all,
>
>I am new to eQUEST and trying to model a VRF
>system. There is no such option, so I think some
>people model it as PVVT. Any suggestions or
>resources on that? Thank you very much.
>
>Regards,
>
>Eleni Soulti
>
>On behalf of
>
>CO2
>Engineering
>
>Oficina Sevilla
>Cartuja - Edificio Marie Curie
>C/Leonardo da Vinci 18, Planta1 3ºB
>41092 Sevilla | España
>T. (0034) 679883055
>
>London Office
>17, Bishops Close
>E17 9RP London | UK
>T. (0044) 7969235926
>
>Oficina Huelva.
>Plaza Hermanos Costalero nº 2, 6º A
>21001 Huelva | España
>T. (0034) 647143558
>
>w. <http://www.co2engineering.eu/>www.co2engineering.eu
>e. <mailto:francisgn at co2engineering.eu>francisgn at co2engineering.eu
>
>
>_______________________________________________
>Bldg-sim mailing list
><http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to
><mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>--
>Chris Flood BSc (Eng)
>Senior Building Analyst
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120928/4683f3b2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 80fa19.jpg
Type: application/octet-stream
Size: 23590 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120928/4683f3b2/attachment-0002.obj>
More information about the Bldg-sim
mailing list