[Bldg-sim] Fan power when changing baseline system per LEED District Energy rules
Bishop, Bill
bbishop at pathfinder-ea.com
Thu Dec 19 06:34:49 PST 2013
Jason,
Per the "Treatment of District or Campus Thermal Energy<http://www.google.com/url?sa=t&rct=j&q=&esrc=s&frm=1&source=web&cd=1&cad=rja&ved=0CCsQFjAA&url=http%3A%2F%2Fwww.usgbc.org%2FShowFile.aspx%3FDocumentID%3D7671&ei=1QKzUuWOBsrokAepk4CIBQ&usg=AFQjCNGNhl9-OMruUu0tuqvHX-iHiN9W3A&bvm=bv.58187178,d.eW0>..." document, p. 10, "Any system parameters not specifically referenced in Table 3 are modeled as specified in Appendix G." I would say that applies to fan power, so your Baseline FCUs should use the System 1 fan power Pfan(w)=CFMS*0.3.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[webCertified_logo_colorRGB72DPI.jpg]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jason Kirchhoff
Sent: Wednesday, December 18, 2013 4:12 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Fan power when changing baseline system per LEED District Energy rules
I'm modeling a multifamily building that uses a campus plant for cooling. I'm familiar with the USGBC document for modeling DES plants, and am currently looking at Option 1, which is an energy neutral purchased chilled water plant. Because the building is residential, the normal baseline system is System 1-PTAC. The USGBC document says to change this to a 4-pipe fan coil in order to make use of the purchased chilled water. Fair enough.
My problem is how to calculate fan power for this new baseline system. FCUs are not a normal baseline system, so there's no direction in Appendix G. Has anyone come across this before? If so, what did you do to calculate the fan power?
For what it's worth, I see three options:
1) Since I'm replacing System 1, use the formula for System 1, Pfan=CFMs*0.3. The resulting fan power is much lower than my proposed, which is a bummer, though it's primarily due to 5 DOAS fans that of course aren't in the baseline.
2) Allow TRACE to calculate the fan power using its built-in 90.1 features. This number comes out much higher than the proposed fan power, which is what tipped me off to this issue. I'm currently trying to back out how Trace arrived at the fan power it did.
3) The proposed building uses fan coils. Since the new baseline also does, set the fan powers equal and only receive credit from reduced run hours due to improved envelope and such. This sounds like a nice way to guarantee reviewer comments.
Any thoughts?
Thanks,
Jason Kirchhoff
Technical Director
Energize Analytics
www.energizeanalytics.com<http://www.energizeanalytics.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/fda7cf54/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/fda7cf54/attachment-0002.jpg>
More information about the Bldg-sim
mailing list