[Bldg-sim] DES Option 1 Pump Power
David Eldridge
DEldridge at grummanbutkus.com
Thu Dec 19 09:29:43 PST 2013
I've been pondering this one as well. I'm imagining that if we say "DES = purchased heat = boiler" then Appendix G would want to have 19 W/gpm pumps primary to the building. But on the other hand, that 19 W/gpm comes from an assumption of a boiler which may have a higher pressure drop than the HX or secondary loop connection in your case. If your proposed building has a secondary loop off of a campus distributed hot water system, then the allowance for 19 W/gpm is probably generous.
The wording is also ambiguous - the building could be considered "primary" if the connection to DES was a heat exchanger rather than a secondary pumping configuration. If you did go to Option 2, then the losses of the steam system or heating hot water system would be accounted for there.
I'd leave the steam vs HW argument out of it - you'd be claiming a pumping energy "benefit" in model space that ignores some real world losses for condensate recovery, losses in the piping, etc. Where the proposed is steam all the way to the coils, I think the baseline should also neglect pumping energy.
The interesting part of this project is that it sounds like it has district steam and primary heating hot water provided to the building? If so then stick with what the reviewer suggested.
If I'm not grasping the scenario and the building receives steam that is used directly in preheat coils and through a heat exchanger to create hot water for use in terminal units, then I think the 19 W/gpm should be allowed for the pumped portion only. I think this would also apply if the heating hot water was through a heat exchanger to allow for pressure drop of the heat exchanger.
What was your W/gpm for the proposed case? If the proposed is way less than the baseline I think we are missing something and the reviewer may be correct.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Thursday, December 19, 2013 9:01 AM
To: Kevin Kyte; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] DES Option 1 Pump Power
Kevin,
Here's my interpretation of the LEED comment: An Option 1 heating loop is equivalent to a primary loop upstream with a secondary loop downstream. However, Appendix G requires heating loops to be modeled as primary-only. The baseline pump power allowance is based on a primary loop only, and there is no way (according to the LEED comment) to separate the primary loop pump power (which is excluded) from the secondary loop pump power. Therefore, the reviewer wants to see identical heating loop pump power in baseline and proposed.
However, in your case, your district/campus loop is a steam loop which you could argue has no pump power, which could potentially justify modeling 19W/gpm for the baseline heating loop and your actual separate steam and HW loops (from a steam-to-HW heat exchanger, correct?) in the proposed. Unless you get a more thorough review comment or find a CIR explaining it better, I would try that approach and explain it in detail with the revised submission.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[webCertified_logo_colorRGB72DPI.jpg]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kevin Kyte
Sent: Wednesday, December 18, 2013 3:43 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] DES Option 1 Pump Power
Hello, I am reviewing an energy model and associated LEED comment for a DES project that is modeled using Option 1 (stand-alone scenario), there is no specific reference to pump power within the guidance document. The LEED comment states:
"Since the project follows the DES guidance Option 1, only the Baseline secondary distribution loop from Appendix G, with the relevant pump and loop parameters from that secondary loop must be modeled. Additionally, since the distribution loop for hot water is a primary-only loop that includes both upstream and downstream equipment, this option is not available for purchased steam or hot water, and the Baseline Case hot water pumps must be modeling identically in the Baseline and Proposed Cases based on the Proposed Case values.
I believe the directive here is to model the baseline pumps identical to the proposed and equal to the proposed values. The LEED review comment states that the loop includes upstream equipment when Option 1 is specifically to exclude upstream equipment and model stand-alone. The energy source is purchased heat.
I think the problem is that I see that the steam coils in the roof-top units are modeled in the same loop as the HW terminal units. If I separate these into two loops I should be able to claim energy savings for the pump power associated with the HW terminal units. Is this correct or is it still required to model the HW terminal unit pump power identical in baseline and proposed cases?
Thank you.
Kevin J. Kyte, PE BEMP LEED AP
WATTS ARCHITECTURE & ENGINEERING
95 Perry Street | Buffalo, NY 14203
Direct: 716 206 5174
Main Desk: 716 206 5100
Fax: 716 206 5199
[http://www.linkedin.com/img/signature/icon_in_blue_14x14.gif]<http://www.linkedin.com/pub/kevin-j-kyte-pe/48/499/29b>Professional Profile<http://www.linkedin.com/pub/kevin-j-kyte-pe/48/499/29b> | www.watts-ae.com
[linkedin]<http://www.linkedin.com/company/watts-architecture-&-engineering> [fb] <https://www.facebook.com/#!/pages/Watts-Architecture-Engineering/268757479845765> [blog] <http://watts-ae.com/blog/> [YouTube] <http://www.youtube.com/user/WattsAE?feature=guide>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/90238b24/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/90238b24/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 146 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/90238b24/attachment-0010.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.gif
Type: image/gif
Size: 1317 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/90238b24/attachment-0011.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.gif
Type: image/gif
Size: 1339 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/90238b24/attachment-0012.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.gif
Type: image/gif
Size: 1071 bytes
Desc: image005.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/90238b24/attachment-0013.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.gif
Type: image/gif
Size: 1139 bytes
Desc: image006.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/90238b24/attachment-0014.gif>
More information about the Bldg-sim
mailing list