[Bldg-sim] Fan power when changing baseline system per LEED District Energy rules
Clark Denson
cdenson at ssr-inc.com
Thu Dec 19 14:21:11 PST 2013
Hi, Jason.
With all due respect to Trane TRACE, I have not found their built-in PRM Fan Calculator to accurately reflect the equations and methods in ASHRAE 90.1, Appendix G, particularly related to the way they handle the 'A' fan power credit. Verify it for yourself, but I would calculate baseline fan power outside the software.
Thanks,
Clark Denson, PE, CEM, BEMP, LEED AP BD+C
SSRCx(r)
(615) 460-0482
From: Dennis Knight [mailto:dknight at wholebuildingsystems.com]
Sent: Thursday, December 19, 2013 10:33 AM
To: Jim Dirkes
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Fan power when changing baseline system per LEED District Energy rules
Jason,
If the DOAS fan power is what is driving you over the top on your proposed model, how are you dealing with outside air in the baseline? If the added energy consumption for the FCU's handling all of the OA without heat recovery in the baseline is not offsetting the DOAS fan power then look at how the FCU fans in the baseline are bing controlled. I would assume since it is a residence or dorm the FCU fans have to run 24/7 at constant volume to handle the required ventilation and the district chilled water and district hot water (if that is your heat source) have to expend a lot more energy to treat the ventilation than the DOAS with heat recovery. Just a thought.
Dennis
On Thu, Dec 19, 2013 at 10:12 AM, Jim Dirkes <jim at buildingperformanceteam.com<mailto:jim at buildingperformanceteam.com>> wrote:
I agree with Bill.
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653<tel:616%20450%208653>
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Bishop, Bill
Sent: Thursday, December 19, 2013 9:35 AM
To: Jason Kirchhoff; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Fan power when changing baseline system per LEED District Energy rules
Jason,
Per the "Treatment of District or Campus Thermal Energy<http://www.google.com/url?sa=t&rct=j&q=&esrc=s&frm=1&source=web&cd=1&cad=rja&ved=0CCsQFjAA&url=http%3A%2F%2Fwww.usgbc.org%2FShowFile.aspx%3FDocumentID%3D7671&ei=1QKzUuWOBsrokAepk4CIBQ&usg=AFQjCNGNhl9-OMruUu0tuqvHX-iHiN9W3A&bvm=bv.58187178,d.eW0>..." document, p. 10, "Any system parameters not specifically referenced in Table 3 are modeled as specified in Appendix G." I would say that applies to fan power, so your Baseline FCUs should use the System 1 fan power Pfan(w)=CFMS*0.3.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[webCertified_logo_colorRGB72DPI.jpg]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004<tel:%28585%29%20325-6004> Ext. 114 F: (585) 325-6005<tel:%28585%29%20325-6005>
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jason Kirchhoff
Sent: Wednesday, December 18, 2013 4:12 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Fan power when changing baseline system per LEED District Energy rules
I'm modeling a multifamily building that uses a campus plant for cooling. I'm familiar with the USGBC document for modeling DES plants, and am currently looking at Option 1, which is an energy neutral purchased chilled water plant. Because the building is residential, the normal baseline system is System 1-PTAC. The USGBC document says to change this to a 4-pipe fan coil in order to make use of the purchased chilled water. Fair enough.
My problem is how to calculate fan power for this new baseline system. FCUs are not a normal baseline system, so there's no direction in Appendix G. Has anyone come across this before? If so, what did you do to calculate the fan power?
For what it's worth, I see three options:
1) Since I'm replacing System 1, use the formula for System 1, Pfan=CFMs*0.3. The resulting fan power is much lower than my proposed, which is a bummer, though it's primarily due to 5 DOAS fans that of course aren't in the baseline.
2) Allow TRACE to calculate the fan power using its built-in 90.1 features. This number comes out much higher than the proposed fan power, which is what tipped me off to this issue. I'm currently trying to back out how Trace arrived at the fan power it did.
3) The proposed building uses fan coils. Since the new baseline also does, set the fan powers equal and only receive credit from reduced run hours due to improved envelope and such. This sounds like a nice way to guarantee reviewer comments.
Any thoughts?
Thanks,
Jason Kirchhoff
Technical Director
Energize Analytics
www.energizeanalytics.com<http://www.energizeanalytics.com>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
--
M. Dennis Knight, P.E., FASHRAE
Founder & CEO
Whole Building Systems, LLC
P.O. Box 1845
Mt. Pleasant, SC 29465
Phone: 843-437-3647
Email: dknight at wholebuildingsystems.com<mailto:dknight at wholebuildingsystems.com>
Website: www.wholebuildingsystems.com<http://www.wholebuildingsystems.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/a9ba4b87/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 3124 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131219/a9ba4b87/attachment-0002.jpg>
More information about the Bldg-sim
mailing list