[Bldg-sim] Appendix G Secondary Pump Control
Christian Kaltreider
ckaltreider at sudassociates.com
Fri Dec 20 08:58:04 PST 2013
Bill,
Thanks. Yes, the 22W/gpm total requirement is still fresh in my mind from
the recent discussion on this forum!
I understand your approach to pump control. But.would you be able to defend
that approach if someone (like your client) pushed you about why you aren't
getting them better savings by running your secondary CHW pump 8760?
Certainly the 90.1 folks had some specific intent, whether they made it
clear or not.
Thanks,
Christian
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Friday, December 20, 2013 10:08 AM
To: Christian Kaltreider; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Appendix G Secondary Pump Control
Christian,
I always model one secondary pump for the baseline. I see no reason to do
otherwise.
My approach to loop activation has been to model it the same as the proposed
design. Using DOE-2 for example, it could be SCHEDULED to run 24/7 during
cooling months, or DEMAND-ONLY to stay off until a coil or process load
exists. If the proposed design has no CHW plant, but has a boiler/HHW plant,
you could model the baseline CHW loop activation similarly to the proposed
HHW loop. If the proposed design has no analogous loop operation, you just
have to make a judgement call, but I am not aware of any guidance in 90.1 or
LEED. Also keep in mind that 22W/gpm is the total pump power allowance for
all your primary/secondary CHW pumps, and not the power of each pump.
Regards,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects
LLP
Senior Energy Engineer
webCertified_logo_colorRGB72DPI.jpg
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
<mailto:wbishop at pathfinder-ea.com> bbishop at pathfinder-ea.com
<http://www.pathfinder-ea.com/> www.pathfinder-ea.com
P Sustainability - the forest AND the trees. P
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christian
Kaltreider
Sent: Friday, December 20, 2013 9:15 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G Secondary Pump Control
I have a question regarding 90.1 2004 Appendix G baseline chilled water pump
control. Section 3.1.3.10 says that baseline CHW systems must be
primary/secondary, with a constant flow primary loop and a variable flow
secondary loop. The secondary pump will either ride the curve or be
controlled by a VSD depending on square footage. In the case I currently
have in my hands, the pump rides the curve. No questions yet.
Section 3.1.3.11 goes on to state that each chiller shall have its own
condenser water and chilled water pumps, interlocked to operate with the
chiller. This is clear and reasonable for the condenser water and primary
chilled water pumps, but what about secondary chilled water pumps? For my
current application (one chiller, pump riding curve), my question simply
boils down to whether I should turn the secondary pump off when the chiller
is off, or if I should run it all of the time.
But to get into it a little more, here are three approaches I see:
1. Model one secondary pump for each chiller, and turn each pump off
when its associated chiller turns off. Section 3.1.3.10 is titled Chilled
Water Pumps, and that section includes both primary and secondary pumps, so
when the next section references "chilled water pumps" that should include
both primary and secondary. However, this does not reflect the typical
reality of one secondary pump serving multiple chillers, and the common
interpretation that only a primary pump has one single associated chiller.
2. Model one secondary pump regardless of how many chillers there are,
and turn it off when all chillers are off. This is perhaps most similar to
what you might expect in a 'real' system. If you only have one chiller (as
I currently have), this is exactly the same as approach 1.
3. Model one secondary pump regardless of how many chillers there are,
and never turn it off. Many buildings are unfortunately operated this way.
This approach significantly increases baseline energy when the pump is
riding the curve.
I have always used approach 2 without putting much thought into it. But now
my results are highly dependent on which approach I take, and I see enough
ambiguity that arguments could be made for approach 3.
Your thoughts?
Thanks,
Christian
Christian Kaltreider, LEED AP | Energy Analyst
Sud Associates, P.A. | T 828.255.4691 | F 828.255.4949 |
www.sudassociates.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131220/a8643186/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3124 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131220/a8643186/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list