[Bldg-sim] Gross cooling capacity at ARI conditions
Kingsley, Michael L.
MICHAEL.L.KINGSLEY at saic.com
Fri Jan 11 06:52:45 PST 2013
Don't forget to deal with the fan heat as well.
gross cooling capacity - fan heat = net (rated) cooling capacity
gross cooling capacity is therefore higher than net capacity, and the
gross EIR will be higher due to both the reduction in electrical input
(fan input taken out) as well as the higher cooling capacity.
Since the fan input energy and heat load are still dealt with, albeit
separately, the net capacity and net EIR are still as expected (rated).
I hope this is clear.
Best regards,
Mike
Michael L. Kingsley, PhD, PE, CPMP, LEED AP
Senior Engineer/Project Manager | Energy Efficiency & Demand Response
SAIC Energy, Environment & Infrastructure, LLC
office: 315.434.7205 | mobile: 315.373.4081
www.saic.com/EEandI <http://www.saic.com/EEandI>
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Thursday, January 10, 2013 1:04 PM
To: Rasheed Ahmad; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Gross cooling capacity at ARI conditions
I'm not terribly satisfied with the clarity of terminology in the
example provided...
The basic concept is "gross (nominal) cooling energy" - "fan energy
input" = "non-fan cooling energy"
Put another way, you can ultimately arrive at a cooling EIR (independent
of fan energies) by subtracting the fan kW from the system total kW at
ARI conditions.
Trying to present this using capacities instead of kW is only confusing
the point they mean to make, as I understand it.
Hope that helps!
~Nick
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [
mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rasheed
Ahmad
Sent: Thursday, January 10, 2013 6:43 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Gross cooling capacity at ARI conditions
Hello All,
>From the user's guide, the fan power should be removed from the standard
EER
rating of packaged cooling systems.
A 15-ton packaged rooftop single-zone system having an EER of 8.6 (COP
of
2.5) is
specified for a building. The following table gives the design
specifications. How should
this be modeled?
Equipment parameter Value
Net Cooling Capacity (Btu/h) 174,000
Total Packaged Unit Input Power (W) 20,128
EER 8.64
Gross Cooling Cap (ARI conditions) 182,000
The supply fan power is the difference between the gross and the net
cooling
capacity.
So my Query is that Gross Cooling capacity ( ARI Condition ) is same for
all Packaged system of any tonnage ??? Is it standard one or what ????
........Like i have 1.5
ton of PTAC system, so for 1.5 ton of PTAC system also its gross cooling
capacity is same 182,000????
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130111/959bcfbd/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130111/959bcfbd/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list