[Bldg-sim] LEED Core & Shell questions
Wealend, Edwin
e.wealend at cundall.com
Wed Jul 31 18:41:47 PDT 2013
Bill,
Response below. Hope that helps!
Regards,
Ed
Edwin Wealend
Senior Engineer
Cundall Hong Kong
T +852 2566 6260
www.cundall.com.hk<%20www.cundall.com.hk%20>
[cid:image001.jpg at 01CE8E9B.54CCDC30]<http://www.linkedin.com/company/cundall> [cid:image002.jpg at 01CE8E9B.54CCDC30] <http://twitter.com/#!/cundall_global>
9th Floor Chinachem Johnston Plaza, 178-186 Johnston Road, Wanchai, Hong Kong, China
香港湾仔庄士敦道178-186号, 华懋庄士敦广场 9楼
Please consider the environment before printing this e-mail
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Wednesday, July 31, 2013 04:11
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED Core & Shell questions
1. Should Tenant Spaces in LEED Core & Shell projects be modeled with Appendix G systems for the Baseline, and for the Proposed as well if there is no HVAC design? – Correct – no profit or loss should be claimed for the HVAC in tenant spaces
-OR- Should Tenant Spaces be modeled as “unconditioned” in both the Baseline and Proposed? (-OR- some other option?)
2. What is the intent/purpose of the requirement to model separate electric meters for lighting, plug loads and process loads in the Tenant Spaces? Should the cost from these meters be removed from the building energy cost for EAc1 savings? – To ensure you’ve applied the same internal gains for the HVAC network to deal with. Arguably you could claim fewer meters would still give you the same information, it’s just gives the LEED reviewer all the info they need.
3. IF HVAC systems are modeled in the Tenant Spaces, should this energy be assigned to separate meters as well? – Yes, particularly if you want to claim the benefit of Landlord controlled energy vs. tenant controlled energy using the Core & Shell Alternative Compliance Path (ACP) – generally worthwhile if the tenant/landlord consumption is about 50/50.
LEED Core & Shell Appendix 2<http://www.usgbc.org/resources/appendix-2-core-and-shell-energy-modeling-guidelines> describes how the HVAC systems should be modeled for the Core and Shell Building, but not for the Tenant Spaces. Appendix 2 also describes the requirement for modeling separate meters.
Thank you,
Bill
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
P Sustainability – the forest AND the trees. P
For further information about Cundall please visit http://www.cundall.com/Locations/Asia/Asia.aspx
--------------------------------------------------------------------------------
Cundall Hong Kong Limited. Registered office: Chinachem Johnston Plaza, 178-186 Johnston Road, Wanchai, Hong Kong.
All information contained in this email is private and confidential, and may also be privileged.
This email and its attachments are intended solely for the use of the addressee only and if any third party whatsoever
comes into possession of this email,they rely on it at their own risk and Cundall accepts no duty or responsibility
(including in negligence) to any such third party.
If you have received this email in error, please immediately notify the sender and delete all copies from your system.
Privacy Policy: Use of this email and any attachments is subject to the terms on our Website at
http://www.cundall.com/Misc/Privacy-Policy.aspx If you cannot access these terms,
please email terms at cundall.com with SEND TERMS in the subject heading or telephone +44 (0191) 213 1515 and we will send you a copy.
All of our business is conducted in accordance with Cundall’s Ethical Business Policy. http://www.cundall.com/Knowledgehub/Ethical-Business-Policy.aspx
--------------------------------------------------------------------------------
This email message has been scanned for viruses by Mimecast. For more information please visit http://www.mimecast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130801/42a6fd9a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 514 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130801/42a6fd9a/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 841 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130801/42a6fd9a/attachment-0005.jpg>
More information about the Bldg-sim
mailing list