Khristiam,
Is it possible that your space has extremely high latent (moisture) loads?
Your results would indicate an SHR (Sensible Heat Ratio) of only around 0.5,
which doesn't seem typical for office occupancies.
e.g., 300 cfm would give a sensible cooling of around 6600 Btu/h. SHR =
6600/12000 = 0.55.
Regards,
LOD
===============================
Larry O. Degelman, P.E., BEMP, HBDP
Professor Emeritus of Architecture
Texas A&M University
===============================
-----Original Message-----
From: Khristiam Alvarez
Sent: Thursday, February 28, 2013 3:10 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] CFM per ton
Dear Sirs
I made a simulation of two one floor building for offices.
The results indicate the following:
Area / Sypply / Design Capacity
2810 sqft / 3974 cfm / 271cfm/ton
1017 swft / 1306 cfm / 302cfm/ton
Why the software gives these results so differente from the usual rule
of thumb 400cfm/ton?
Thank you very much.
--
Khristiam Alvarez
Ingeniero Mecánico
Proyecto Hidroeléctrico Tocoma, Módulo 4
Proyectos Mecánicos
Estudios e Ingeniería de Expansión
CORPOELEC
Km. 85 Vía Guri, Mun. Angostura, Edo. Bolivar, VENEZUELA
Tlfs: 0286.965.3579 / 0424.9701025 / 0416.5861057
Para llamar desde fuera de Venezuela:
+58.286.9653579 / +58.424.9701025 / +58.416.5861057
"Este contenido es confidencial y de interes exclusivo para el Ministerio
del Poder Popular para la Energia Electrica (MPPEE) y sus entes adscritos,
por lo tanto, se permite copiar o distribuir el mismo solo a personas
autorizadas. Si recibe este correo por error, por favor destruyalo y
notifique al remitente. Eventualmente, los correos pueden ser interceptados
o alterados, llegar con demora o incompletos, al respecto el MPPEE y sus
entes adscritos no se hacen responsables por los errores, defectos u
omisiones
que pudieran afectar al mensaje original."
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.2897 / Virus Database: 2639/6124 - Release Date: 02/22/13
More information about the Bldg-sim
mailing list