> Leen,
>
> Barring places with geothermal hot spots, ground temperatures are
> calculated using a simple equation developed by the late Dr. Tamami Kusuda
> at NBS (National Bureau of Standards, now renames NIST National Institute
> of Science and Technology) in the early 1970's that assumes a constant deep
> ground temperature of the average annual air temperature + 1 K. This
> equation is basically a sine curve that dampens and lags the annual air
> temperature profile depending on the soil conductivity and depth below the
> surface.
>
> All that is worked out in any of the processed weather files, such as the
> IWEC2 weather files available from ASHRAE for $229 for the entire set of
> 3,012 or individually from my company for $35 a station. For your location
> (Nador), the closest IWEC2 weather file is for Melilla 8 kilometers to the
> north, for which the monthly ground temperatures at 1 meter below grade are:
> 16.7 15.7 15.6 16.1 18.0 19.9 21.5 22.6 22.6 21.8 20.2 18.4
> (converted to Celsius from Rankine in DOE-2 *.BINM weather file for
> Melilla)
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 108D
> Moraga CA 94556yjhuang at whiteboxtechnologies.comwww.whiteboxtechnologies.com
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
>
> On 3/5/2013 12:16 PM, leen peeters wrote:
>
> Dear simulators,
>
> I am looking for a ground temperature file of Morroco, city of Nador in
> the North of Morocco.
> I want to use this as input for a ground source heat pump.
>
> Leen
>
>
>
> _______________________________________________
> Bldg-sim mailing listhttp://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130305/6ea6fba2/attachment-0001.htm>
More information about the Bldg-sim
mailing list